Ken said:
I think that they design and build their systems to meet their or
their corporate customer's needs, in line with what they may be
willing to pay. In the case of submarines it would be more
whatever is needed, for national defense, regardless of the cost.
In any case, they can pretty much afford any battery they can
dream up, the average DIY homepower, doesn't have that luxury.
My point was that because of that last factor they are able to use
materials and equipment that would never be available to anyone
designing and constructing their own Homepower solutions.
"Station batteries" are a widely available technology. Single 2.1VDC cells
of a wide variety of A-H ratings are commercially available. Probably a
size for just about any homepower installation.
Also
that they can design for a prescribed maintenance environment,
that again includes resources beyond that likely for the Homepower
enthusiast. (I have trouble getting the kid to mow the lawn, once
every blue moon; wouldn't want to consider the results of expecting
him to play Plant Engineer.)
True, maintaining batteries is more work than maintaining a grid-connect
electric meter. But this is true of *any* battery installation. Then it
becomes a question of how valuable your time is, playing Plant Engineer
versus buying new batteries every two or three years.
For the 430v commercial UPS you described "36 12v batteries
connected in series", are we to assume that they had a 430vDC
inverter, that provided a voltage and current capacity to run the
commercial installation? Do you think that if the commercial firm
could not afford that 430v DC inverter, they would have gone with
that design?
Obviously the customer considered the cost of the UPS against the costs of
losing power. Can't speak to that much as I'm not that customer.
We recently 'retired' a UPS at work because a) The cost of replacing the
battery every five years was getting kind of expensive (~$9,000) b) the
annual maintenance /repair was running rather high and c) the 'fragile' (and
costly to repair) computer systems it was protecting had been replaced with
cheaper, COTS PC-based computers. The loss of service had never been the
issue, but the cost of repairs to the 'fragile' computer system after a
power outage. With that risk eliminated, the cost of the UPS was no longer
justifiable.
Then there is the question of what is appropriate for the
scale of the project. Any significant commercial operation
will consume a great deal more energy than the average
wasteful American home; the successful Homepower setup
uses less power than the average wasteful American home.
The design requirements aren't at all the same.
So don't use a submarine battery for a homepower setup. I never actually
suggested that you should. I only pointed out that large commercial setups
of batteries have always opted for series strings of relatively higher
voltage instead of many parallel batteries at low voltage.
When unltra-reliability is an issue, commercial installations will use two
strings in parallel. They aren't paralleling the strings for added
capacity, they are concerned with *redundancy*.
Of course you don't need as many amp-hours as a commercial UPS operation.
But the basic principles are the same, correctly sized cells connected in
series to attain the desired working voltage. The TCO of such a setup is
lower than massively paralleled systems at low voltage. YMMV.
Still lead acid? Not some of the newer much more expensive
exotic batteries? They should want to gain the space savings
if nothing else. In anycase, I haven't seen any sub battery banks
available at my local government surplus auctions, and short of
that I will have to use what is available, and affordable.
I'm sure that small research subs and such use all sorts of exotic power
schemes. But your basic warship submarine sticks to what works.
And again, I never suggested that a submarine battery was the right battery
for a homepower installation. I pointed out that some of the largest
capacity battery systems in use do *not* go for multiple parallel strings.
So *they* (the ever infamous 'they') have figured out that if you want more
capacity, the best way to do it is with larger amp-hour rated cells, *not*
paralleling small cells together.
So you see the homepower guy, being able to afford
the products of Co-Generation contractors?
Just glancing around at random,
http://search.altenergystore.com/energy/rolls surrette
Prices seem to run about $1 / Ah with 10 year warranty. Some higher for odd
voltages, a couple lower.
For a 'golf cart' battery, the first hit I found was...
http://www.apexbattery.com/mk-8agc2-golf-cart-battery-6v-220ah-golf-cart-batteries-.html
Price is a bit over $1 / Ah with a 1 year warranty.
Of course this was just a five minute search. I'm sure a more detailed
search would be appropriate before jumping on any choice.
I think there are already postings and links posted, in this thread,
that bring your "Just about every commercial battery bank is strickly
a single string in series." statement into question. There is also
the fact that "battery banks" come in all sizes, to serve many
different power storage requirements. (While it seems to be my fate
to run into those who think this way
You can't just pick the largest or
most extreme example you know anything about, and say all must
conform to that design.
True, some commercial installations will use two strings in parallel. But
they generally do that for redundancy and reliability. Not for increased
capacity. Different reason all together that probably doesn't apply to a
homepower installation.
daestrom
P.S. Despite our disagreements, it's nice to find someone that is polite
about disagreeing