John Stumbles
[I tried this query on the uk.d-i-y newsgroup without getting a solution.
I'm x-posting it there for info to that group as I hope it may be useful
to others, with followups to s.e.d]
I need to fix up proper controls on a wet (what I think leftpondians call
'hydronic') Central Heating system that has separate pumps driving the
space heating (CH) and water heating (DHW) systems. Each part of the
system has a time switch and thermostat determining when the pump for that
system's hydronic circuit needs to be driven. When the CH or (Boolean-OR)
DHW systems are running the boiler must also run. The boiler has a
'Switched Live' terminal which, when energised, causes it to run.
I know I can do it with 2 relays with their contacts wire-ORed to drive
the boiler Switched-Live:
<pre><tt>
L -----------+--------------------------+-------------+--------------+
| | | |
o | o | o | o |
| CH - programmer - HW | | A | B
o | o | o | o |
| | | |
| | | |
| | +-----------+--+
o | Room o | HW |
| thermo | cylinder |
o | -stat o | 'stat |
| | ----------
| | | SL |
+----+----+ +----+----+ | |
| | | | | boiler |
| ----- | ----- | |
pump (>) | RLA | pump (>) | RLB | | N |
| ----- | ----- ----------
| | | | |
N ------+---------+----------------+---------+---------------------+
However I think I've seen somewhere a single relay solution (but can't
remember where!). The only way I can think of doing it would be to wire
the relay coil between the live terminals of the two pumps which I suppose
would work but seems inelegant.
240V~
L -----------+--------------------------+-----------------------+
| | |
o | o | o |
| CH - programmer - HW | | A
o | o | o |
| | |
| | |
| | |
o | Room o | HW |
| thermo | cylinder |
o | -stat o | 'stat |
| | ----------
| ----- | | SL |
+---------| RLA |----------+ | |
| ----- | | boiler |
| | | |
(>) pump pump (>) | N |
| | ----------
| | |
N -----------+--------------------------+-----------------------+
I'm x-posting it there for info to that group as I hope it may be useful
to others, with followups to s.e.d]
I need to fix up proper controls on a wet (what I think leftpondians call
'hydronic') Central Heating system that has separate pumps driving the
space heating (CH) and water heating (DHW) systems. Each part of the
system has a time switch and thermostat determining when the pump for that
system's hydronic circuit needs to be driven. When the CH or (Boolean-OR)
DHW systems are running the boiler must also run. The boiler has a
'Switched Live' terminal which, when energised, causes it to run.
I know I can do it with 2 relays with their contacts wire-ORed to drive
the boiler Switched-Live:
<pre><tt>
L -----------+--------------------------+-------------+--------------+
| | | |
o | o | o | o |
| CH - programmer - HW | | A | B
o | o | o | o |
| | | |
| | | |
| | +-----------+--+
o | Room o | HW |
| thermo | cylinder |
o | -stat o | 'stat |
| | ----------
| | | SL |
+----+----+ +----+----+ | |
| | | | | boiler |
| ----- | ----- | |
pump (>) | RLA | pump (>) | RLB | | N |
| ----- | ----- ----------
| | | | |
N ------+---------+----------------+---------+---------------------+
However I think I've seen somewhere a single relay solution (but can't
remember where!). The only way I can think of doing it would be to wire
the relay coil between the live terminals of the two pumps which I suppose
would work but seems inelegant.
240V~
L -----------+--------------------------+-----------------------+
| | |
o | o | o |
| CH - programmer - HW | | A
o | o | o |
| | |
| | |
| | |
o | Room o | HW |
| thermo | cylinder |
o | -stat o | 'stat |
| | ----------
| ----- | | SL |
+---------| RLA |----------+ | |
| ----- | | boiler |
| | | |
(>) pump pump (>) | N |
| | ----------
| | |
N -----------+--------------------------+-----------------------+