| A three phase motor can be started at 'full voltage', but depending on size,
| supply considerations and such, often a 'reduced voltage' starting is used.
| One 'reduced voltage' method is to have all six leads (two for each phase)
| of the motor winding brought out to the controller. If the motor is
| designed to work as 480V delta, the starter can temporarily connect the six
| leads of the motor as star. So each winding only sees 277V. After the
| motor accelerates (as determined by... tach, current level, simple
| time-delay or other method), the starter 'breaks' the star at the center and
| connects those three leads to an appropriate phase so the motor is now
| connected 480V delta. Needless to say, one has to be careful to interlock
| the star and delta contactors so they don't pick up at the same time (would
| result in short). And the phase connections have to be correct so the motor
| doesn't try to reverse direction when switching from star to delta.
Wouldn't a 3-pole double-throw contactor be sufficient for that? Since each
winding is going to have one wire connected to a phase line, the other would
go to the contactor, which in one state connects them all to neutral, and in
the other, to the next phase, which will give either a plus 30 or a minus 30
degree phase angle change, depending on which way you go.
While one could "lashup" a home brew Wye-Delta reduced voltage starter, the
consequences of the home brew going South, or the liability issues if one
were to injure property/personnel while doing so, are more than most
reasonable people would risk.
Most commercial Wye Delta starters are interlocked both electrically and
mechanically for obvious reasons, and could also be of the open/closed
transition type.
The links below might be helpful in understanding the theory of Wye Delta
Starters.
http://www.usmotors.com/products/ProFacts/1-120-7.htm
http://www.squared.com/us/products/nema.nsf/bce2f96988bd1a338625643a006e3b29
/32451b329addd9bf85256712005af2f4/$FILE/C_50006-026-01.pdf
I'm sure that Google has many others.
Louis--
Remove the two fish in address to respond