I have a 240 volts GE Smart Water Heater. GE50T6EA
Specs shows it's a dual element
Upper 4500 watts
Lower 4500 watts
---------------------
Total 4500 watts (uncertain why total shows 4500 watts since it's 2 x 4500 watts)
Wire connections on top are a red wire and a black wire. The wire connection lid has a green ground screw.
From what I've read
AC compressor or a water heater do not require a neutral so 2 hots and a grounding means are all that is needed
My wiring cable is 10-3. So all I need to do is connect the two hots to the black and red and my bare ground wire to the green screw and cap off the neutral?
Also I'm currently using 10-3, however the installations manual diagram shows to use 8 gauge copper wire with a 50 am breaker.
I currently have a short run less than 10 feet using 10-3 and a 40 amp dual pole breaker.
I probably should upgrade a no. 10 - 8 gauge copper and a 50 amp dual pole breaker?
Specs shows it's a dual element
Upper 4500 watts
Lower 4500 watts
---------------------
Total 4500 watts (uncertain why total shows 4500 watts since it's 2 x 4500 watts)
Wire connections on top are a red wire and a black wire. The wire connection lid has a green ground screw.
From what I've read
AC compressor or a water heater do not require a neutral so 2 hots and a grounding means are all that is needed
My wiring cable is 10-3. So all I need to do is connect the two hots to the black and red and my bare ground wire to the green screw and cap off the neutral?
Also I'm currently using 10-3, however the installations manual diagram shows to use 8 gauge copper wire with a 50 am breaker.
I currently have a short run less than 10 feet using 10-3 and a 40 amp dual pole breaker.
I probably should upgrade a no. 10 - 8 gauge copper and a 50 amp dual pole breaker?