Cydrome Leader wrote:
Cydrome Leader wrote:
[email protected] wrote:
*+-even the cheap suppressors I've bought had 3 MOVs,one for each leg to
*+-ground and from one leg to the other. I guess that's a "delta" config.
Do surge supressors exist for two-line phone connections?
WOuld it make sence to put a surge suppressor (what kind?) on my
incoming phone line? Neighbors have complained of fried modems, but
curiously I don't remember anyone ever telling mtheir computer got fried.
There should already be one inside the phone company's Network
Interface.
This applies to the US-
there are surge and lightning arrestors on phone lines where they enter a residence, and they're
grounded to something good, like a water pipe for instance.
It works great.
Some comments are somewhat specific to the US.
A couple of excellent sources of info on surge protection are:
<
http://www.mikeholt.com/files/PDF/LightningGuide_FINALpublishedversion_May051.pdf>
from the IEEE, and a much simpler one from the US-NIST
<
http://www.nist.gov/public_affairs/practiceguides/surgesfnl.pdf>
With a strong surge current to the earthing electrode, the "ground" for
the building can rise thousands of volts above "absolute" earth
potential. You want power and phone (and cable) wires rise together.
That requires a short ground wire from the telephone entrance protector
to the earthing system at the power service.
Now if lightning surges hit your power then what happens?
a cheapo-garbage "surge protector" like a power strip or the like will use MOVs to short out line
to neutral or even line to ground.
What happens if you throw a short across line to ground and can somehow clamp it to 600 volts or
whatever? The numbers are made up, but concept is the same.
well, your ground ends up at 300 volts above actual earth ground where that device is located. This
assumes your ground has the same impedance as the current carrying conductors.
So now your computer isn't really grounded, and floating at a potential way off what the phone like
is at, which worst case is being protected to a really solid ground, and not hundreds of feet or
wiring in your walls or whatever.
This is what blows up stuff like modems or devices that sit between your outlets and a phone line.
If you RTFM, any competent plug-in suppressor manufacturer should tell
you the phone wires have to go through the suppressor along with the
power wires. The voltage on all wires is clamped to the ground at the
suppressor. The voltage between the wires to the protected equipment is
safe for the protected equipment. All interconnected equipment needs to
be connected to the same suppressor, or external wires, like cable need
to go through the suppressor. This is clearly explained in the IEEE
guide starting pdf page 40, and shown in the examples at the end.
Plug-in suppressors work primarily by clamping, not earthing.
The best move is to install a service entrance surge supressor. They'll clamp surges at the best
ground you've got, with the lowest possible impedance, and at your ground/nuetral bonding point not
at your load where any attempts to do so are pretty useless across the extra fraction of an ohm.
Service panel suppressors are a real good idea. I would particularly use
one in high risk areas like Florida.
But from the NIST guide:
"Q - Will a surge protector installed at the service entrance be
sufficient for the whole house?
A - There are two answers to than question: Yes for one-link appliances
[electronic equipment], No for two-link appliances [equipment connected
to power AND phone or cable or....]. Since most homes today have some
kind of two-link appliances, the prudent answer to the question would be
NO - but that does not mean that a surge protector installed at the
service entrance is useless."
The NIST guide suggests most damage results from high voltage between
power and phone/cable wires. A service entrance suppressor does not, by
itself, limit that voltage.
You can easily test the resistance of your wiring at home too, and at the same time actually test
if your ground is solid.
connect some large resistive loads like halogen lamps, hairdryer, toaster oven or whatever at and
outlet. Measure the voltage drop when it's on. Break out the suicide cables and test that same
device using line to ground.
Depending on how your place is wired, you may find that under an actual load, your ground is really
awful. A volt meter won't pick crappy ground connections unless you are actually running real
current through it, so just reading 120 across hot and ground and saying "looks good" really
doesn't count.
May well be worthwhile. But even with a good earth connection the
building ground can rise thousands of volts.
Trying to suppress a surge with a $4 power strip connected though 5 junction boxes connected with
BX cable can really just be a big joke.
Neither the IEEE or NIST agree. Both guides say plug-in suppressors,
used correctly, are effective. Plug-in suppressors with very high
ratings are readily and cheaply available. In the US you should only buy
suppressors listed under UL1449. UL tests include a testing to at least
a minimum floor of protection. UPSs with surge protection should also
have UL1449 listing.
The lab NIST uses is not the typical home people live in.
I have no idea what you are talking about. The discussion is ordinary
surge suppressors
yes, ordinary surge surpressors. go to the store, pick one up and tell me
what you find inside of it.
I'd be pleased to counter with the CPSC recall notice.
Have you opened a "surge supressor" that the average person owns? It's
really surprising more don't catch on fire with no surges.
the construction quality tends to really really suck.
Even "name brand" items from tripp-lite are utter pieces of crap for the
most part. I've seen those catch fire, and these were made in USA ones.
I don't use or trust cheap-o power strips, at all, anywhere.
So don't get "cheap-o power strips". I use name brand suppressors with
high ratings.
UL1449 has, since 1998, required thermal discoinnects for overheating
MOVs. If a suppressor is UL1449 listed there is not much probability of
any problem. The author of the NIST guide has written "In fact, the
major cause of [surge suppressor] failures is a temporary overvoltage,
rather than an unusually large surge". TOV is, for example, a
distribution wire falling onto the secondary wires that go to your house.
Again, if you really trust any UL markings on a power strip, go for it.
You do relized that UL doesn't even test most stuff, they sell stickers.
That's the business model. If you want to get more technical, they're
really a licensing company.