simple DC current sensing
Rob Votin
I am trying to find a simple way to detect the presence of a DC
current. Its an industrial application where I need a PLC to be able
to know if current is flowing to several 24 volt electromagnetic
brakes (about 1 or 2 amps each).
Cost is not really an issue, but ideally this would be some small off
the shelf device (inductive or hall effect?) that could directly send
a signal to 24 volt PLC input card. I dont want to use shunts, and I
dont want to have to add an analog input card to the PLC rack.
Everything I've found on the web is either for AC only or puts out an
analog signal proportional to the current. I just want a simple on or
off. Any ideas? Thanks...
Rob
John Popelish
Rob
You might search the key words [DC current switch].
I found:
http://www.controlsupply.com/itm00038.htm
http://www.crmagnetics.com/newprod/ProductView.asp?ProdName=CR5395
Of course, you could just wrap a few turns of wire around the glass
capsule of a reed switch.
j.b. miller
If you can afford a 2 volt drop in the power line to the load, just add a
'module' consisting of 3 power diode in series ,paralleled with an
optocoupler an 10 r current limiting resistor.
Feed the opto transistor to the PLC as a 'current to load' indicator.
have used this setup for years, rock stable,small,cheap,etc. made my own
load indicating SSRs as well......
hth
jay
scada
Rob
I received some samples not to long ago for a hall IC device. It will take
up to 50A DC, and gives a linear 0-5V DC output isolated to something like
3KV. I don't remember the name, but I can get it when I return to the office
on Monday if your interested. I received like four samples, they sell for
somewhere around $8 if I remember right.
legg
You already have a signal; the voltage on the solenoid coil. Perhaps
you think the signal connection for this is too long, and you're
worried about open connections to the solenoid itself, or the sensing
voltage connection.
I'm not sure how you envision this (these) device(s) fitting into your
wiring. It would seem to make more sense if the PLC solenoid driver
card could sense this directly, without external interference.
Over-current and under-current sensors are available from most relay
mfrs. These have all of the problems of getting accurate and
repeatable results from any electromagnetic actuator, unless they
include other powered circuitry for measurement and control of the
terminals. Clare offers app notes on winding your own reed relays,
that could produce the lowest series voltage drop.
A diode drop is sufficient to generate a 24V signal from a bipolar
transistor that current is flowing in the solenoid wire, using the
same voltage that powers the solenoid to get the voltage swing that
the PLC input module expects. Two diode drops would be enough to power
an opto isolator, three; an fet, four; a conventional 5V relay coil.
Having to make an assembly of these sensors, with contacts, is
something that the use of the PLC and its available modules is
intended to avoid in the first place.
If you actually want to know that the solenoid has done its job,
you're talking motion sensors, actuators or auxiliary switches built
into the solenoid assembly.
RL
Rob Votin
Thanks, but I've come across similar devices as that already. LEM
makes them, and possibly others. Problem is, I would then need to
include an analog input card, or other handbuilt circuitry to buffer
the signal and detect a threshold etc...
The whole reason i need this is that the machinery to be controlled
is quite a distance away from the control cabinet, in a a very
hostile enviroment. Wiring faults are common, and it is real important
to stop the process if brakes should fail to release properly
scada
Have you looked at www.weidmuller.com I have used current sensors from them
before. Most of there devices are din rail mounted, and interface with
PLC's.