A GSHP installer grossly undersized the vertical loop field on my system
and won't make it right (yes, I have offered to pay), so I'm left with
looking for alternate solutions. Bear with me on this question, as it
might be educational for other GSHP installers as it's not your typical
home-owner question. Also, for any of you prospective GSHP buyers - don't
belive the claims of 100ft/ton for a vertical direct exchange system.
Unless you're only running the system for an hour or two per day, the
ground will quickly freeze and you'll get half the rated heat out of the
system.
The 4-ton direct exchange system was installed with four, 100ft ground
loops. Ground is solid granite from 8ft down. Loops backfilled with sand.
Normal ground temperature is ~50F. Operational ground temperature runs
from 43F to <32F within 12 hours of operation.
With this system, the loops freeze after one day of normal winter use,
reducing BTU output of the system to <30,000 BTU/h, so system therefore
has to be cycled, day of use, day of rest, to provide the loop field time
to recover back up to around 43F and thence be able to produce closer to
40,000 BTU/h. Still far less than the rated 48k BTU/h.
Options are:
1) add vertical ground loops - this requires getting the original
installer involved again, and they have done a "hit-and-run", refusing to
return my calls, so this is a non-option.
2) add some system to replenish some of the energy extracted from the loop
field
3) deal with it - not acceptable. The system runs decent when the ground
temp is >40F, so I want to salvage it.
Evaluating options, I've been looking at (2) - how to replenish the energy
extracted from the loop field. This brings up other options
1) Run open loop - add running water to the vertical loops to bring in
ground temperature water. At 8-10gpm, at a dT of 10F, this would bring in
40-50k BTU/h.
Problem with this - I would have gone this way originally if i had a water
source capable of supplying that much water. a 950ft well on the property
yields only 1.25gpm.
2) Run solar and pump the heat into the loop field.
This is an intriguing idea, but at roughly 25kBTU per DAY per panel, it's
not practical. During the winter, the system is extracting 300-400
kBTU/day at 50% run time. It would definitely help though and is
advantageous because it's renewable. On the downside, this won't help in
the Summer when the loop field heats up and is unable to keep up with the
home's cooling load.
3) Run solar and heat the house directly with it.
If one installs solar hot water panels, may was well put it to direct use
and add radiant heating where possible in the house. This would directly
reduce the percent on-time of the GSHP and hence put less strain on the
loop field.
Same disadvantage as (2) in that it doesn't help during the Summer.
4) Add a horizontal slinky field, and circulate the heat transfer fluid in
the vertical loop field.
This option works by my calculations. Adding four loops and circulating
the fluid from each of these (closed) loops down alongside the exising
vertical loops can provide ~15kBTU/h per loop at a flow rate of ~3gpm with
a dT of 10F. Subtract off for inefficiencies, and it seems that this is
just about the right capacity to achieve the balance point.
I still need to compute the energy capacity of the ground in the slinky
field as obviously it will get colder as the energy is pumped out.
However, at the very least, it should greatly reduce the load on the
vertical loop field since granite has a Cp of about the same as sand, and
considerably less than clay or moist soil.
an added downside is the energy consumption of the circulator pumps.
Circulating 3gpm through 1000ft of 3/4" PEX requires a fairly hefty
capacity, I'm calculating a pump head pressure of 55-60 ft. (depending on
the viscosity of the transfer medium), though I'm not positive about that
figure. That would be times 4 to get the desired overall system energy
transfer. So If one has to run an extra kilowatt of pump to circulate
enough medium, that's going to largely negate the benefits of the added
COP yielded by heating the ground. Though it would be feasible to add PV
panels and just run the circulators while the sun is out, though Ideally
you'd want to run them when the load is highest.
If this all sounds like a Kluge, I agree. During the lead-up to the
install, I had been questioning the manufacturer about exactly these types
of questions because I was dubious about their claims that 100ft/ton was
adequate. I'd actually upgraded and ordered the 150ft/ton system but the
installer broke his drilling rig during install and insured me that the
system wouldn't suffer by dropping back to 100ft/ton.
So there's the situation. Can anybody add to this equation (other than
telling me that I've been robbed)?
tia.
and won't make it right (yes, I have offered to pay), so I'm left with
looking for alternate solutions. Bear with me on this question, as it
might be educational for other GSHP installers as it's not your typical
home-owner question. Also, for any of you prospective GSHP buyers - don't
belive the claims of 100ft/ton for a vertical direct exchange system.
Unless you're only running the system for an hour or two per day, the
ground will quickly freeze and you'll get half the rated heat out of the
system.
The 4-ton direct exchange system was installed with four, 100ft ground
loops. Ground is solid granite from 8ft down. Loops backfilled with sand.
Normal ground temperature is ~50F. Operational ground temperature runs
from 43F to <32F within 12 hours of operation.
With this system, the loops freeze after one day of normal winter use,
reducing BTU output of the system to <30,000 BTU/h, so system therefore
has to be cycled, day of use, day of rest, to provide the loop field time
to recover back up to around 43F and thence be able to produce closer to
40,000 BTU/h. Still far less than the rated 48k BTU/h.
Options are:
1) add vertical ground loops - this requires getting the original
installer involved again, and they have done a "hit-and-run", refusing to
return my calls, so this is a non-option.
2) add some system to replenish some of the energy extracted from the loop
field
3) deal with it - not acceptable. The system runs decent when the ground
temp is >40F, so I want to salvage it.
Evaluating options, I've been looking at (2) - how to replenish the energy
extracted from the loop field. This brings up other options
1) Run open loop - add running water to the vertical loops to bring in
ground temperature water. At 8-10gpm, at a dT of 10F, this would bring in
40-50k BTU/h.
Problem with this - I would have gone this way originally if i had a water
source capable of supplying that much water. a 950ft well on the property
yields only 1.25gpm.
2) Run solar and pump the heat into the loop field.
This is an intriguing idea, but at roughly 25kBTU per DAY per panel, it's
not practical. During the winter, the system is extracting 300-400
kBTU/day at 50% run time. It would definitely help though and is
advantageous because it's renewable. On the downside, this won't help in
the Summer when the loop field heats up and is unable to keep up with the
home's cooling load.
3) Run solar and heat the house directly with it.
If one installs solar hot water panels, may was well put it to direct use
and add radiant heating where possible in the house. This would directly
reduce the percent on-time of the GSHP and hence put less strain on the
loop field.
Same disadvantage as (2) in that it doesn't help during the Summer.
4) Add a horizontal slinky field, and circulate the heat transfer fluid in
the vertical loop field.
This option works by my calculations. Adding four loops and circulating
the fluid from each of these (closed) loops down alongside the exising
vertical loops can provide ~15kBTU/h per loop at a flow rate of ~3gpm with
a dT of 10F. Subtract off for inefficiencies, and it seems that this is
just about the right capacity to achieve the balance point.
I still need to compute the energy capacity of the ground in the slinky
field as obviously it will get colder as the energy is pumped out.
However, at the very least, it should greatly reduce the load on the
vertical loop field since granite has a Cp of about the same as sand, and
considerably less than clay or moist soil.
an added downside is the energy consumption of the circulator pumps.
Circulating 3gpm through 1000ft of 3/4" PEX requires a fairly hefty
capacity, I'm calculating a pump head pressure of 55-60 ft. (depending on
the viscosity of the transfer medium), though I'm not positive about that
figure. That would be times 4 to get the desired overall system energy
transfer. So If one has to run an extra kilowatt of pump to circulate
enough medium, that's going to largely negate the benefits of the added
COP yielded by heating the ground. Though it would be feasible to add PV
panels and just run the circulators while the sun is out, though Ideally
you'd want to run them when the load is highest.
If this all sounds like a Kluge, I agree. During the lead-up to the
install, I had been questioning the manufacturer about exactly these types
of questions because I was dubious about their claims that 100ft/ton was
adequate. I'd actually upgraded and ordered the 150ft/ton system but the
installer broke his drilling rig during install and insured me that the
system wouldn't suffer by dropping back to 100ft/ton.
So there's the situation. Can anybody add to this equation (other than
telling me that I've been robbed)?
tia.