| |> And once you have the CTs installed and shorted, how do you go about using
|> them? Do you now un-short them? While the power is still up?
|
| If you have to ask, then you better get someone knowledgeable to do this for
| you. CTs produce lethal voltage across an open secondary when current flows
| through the primary side. The shorting bar prevents this until the meter is
| connected.
Well, that's two people that misunderstood my question. So I guess it's my
fault for wording it badly. So I will try it from another angle:
Why is it safe to unshort the secondary once the meter is attached?
The question you ask makes it clear you do not understand
how to use CT's. That is not said as an insult, but rather
to underscore what other's have told you: you need to get
someone who knows CT usage to help you out. I'll try to
shed some light on it - but *please* don't mess with these
unless you know before hand exactly what will happen.
Think of the whole circuit, in "electronic" detail:
CT=======Meter is, electronically, the secondary of
a transformer with a resistance connected across it,
so it can be redrawn as CT=====R
The CT is designed to achieve a specific current
(NOT a specific voltage as in a "regular" transformer)
in the secondary when a specific current flows in
the primary. This concept sometimes causes those
learning about CT's some difficulty, but it is
critical to understand it: a current will exist
in the secondary with or without a load connected
to the secondary.
Now, that current transformer will produce some
specific current when a specific current flows in
the primary. Lets use the 2.5 amps as the current
produced. What value of R is required to keep the
voltage safe? Assume whatever voltages you want,
within reason, and work ohms law to get a feel for
how the voltage changes depending on the resistance.
Say, for example, the resistance is 1 ohm. The voltage
therefore has to be 2.5 volts. Now assume that the
resistance is 11 megohm, as it would be if you wrongly
set the meter (DMM) to the voltage scale. Remember,
E = IR, so E would equal 2.5 amps times 11,000,000
ohms!
If you use the meter properly, it would be set
on the amps scale, where a low resistance shunt
is connected in the circuit. That shunt is why it is
safe to remove the shorting bar with the meter
properly connected.
There is another circuit to consider:
CT====BurdenResistor====meter.
In the above case, the burden resistor keeps
the voltage low, and the meter can be, and is,
used on the voltage scale.
Bottom line - you never want a current transformer
on an energized circuit without either a proper
load or a shorting bar connected across the
secondary. An open, or improperly loaded secondary
circuit on a CT is a definite "NO-NO".
And: what is the voltage?
The output of a CT is a specific value of current
for a specific input current - the secondary
CURRENT is proportional to the primary CURRENT.
The primary voltage is fixed, and the primary
current varies. The secondary current varies
when the primary current varies. The secondary
voltage depends on the secondary current AND
the resistance connected across that secondary.
See, that's the thing. When using CT's *you*
need to select the voltage. You either make
it low enough where you don't care about it
at all (with a shorting bar), or you select it
and design it into the system by proper selection
of the burden resistor. You need to understand
this and be able to do it before you can mess
with the things safely.