On Tue, 10 Feb 2004 05:38:34 GMT
[email protected] wrote:
... You might say it is safer to insert a "resistor" of 0.0001
ohms and measure the voltage drop across it. Perhaps so.
Actually, quite often an in-line resistor/shunt is *not* safer. If the
primary circuit is high-voltage, the leads used to sense the voltage drop
across the shunt will also be at line voltage. One of the advantages of
CT's is the secondary circuit is *low* voltage (<=120) and is easier to run.
.... So why do all the CT ratios I see
are compared to 5 instead of 1? That's not theory; it's practice (and I
don't yet know why).
True, it is 'practice', not 'theory'. The 'practice' is that most
commercial metering use 5 amp current circuits. A typical kW or MW meter
will be designed for 120V and 5A at the meter terminals. So most PT's are
ratio of said:
So why do we have 110-120 volts in the US, and they
have 220-240 volts in Europe? Physics won't decide that; politics does.
It may have been the "politics" of a few engineers at power companies. I
do know Edison's first DC system was 110 volts, so that could certainly have
set a precendent (an AC system replacing it would prefer the same voltage to
use the same light bulbs ... that's compatibility ... as practical as it is,
it's still politics).
This is probably the 'most correct' answer for why we have 120/240 in US.
My question was one of practices ... a politics category. And apparently
one that some engineers want to keep others from learning about ... perhaps
to protect their jobs.
Occam's razor. Don't assume nasty conspiracies when the simpler answer is
you just haven't made your question clear enough for people to understand.
I'll ask it again in a different form, focusing on specifics that were not
clear before. How do you verify that it is safe to remove the shorting bar
on a CT secondary when the circuit it is monitoring is energized and loaded,
and you can't measure that you get the correct resistance across the burden
resistor, and was not damaged into an open condition during installation,
when an ohm meter test would show zero due to the shorting bar still present?
You don't. You have to make the initial installation with the system dead.
As part of the initial checkout, you verify the shorting links work
correctly. If you have to work on the metering, you either kill the
circuits, or trust that the shorting links still work correctly. If you
have any doubt about the shorting links, you don't trust them and have to
reschedule the work when the system is dead.
If the shorting links are separate from the meter and normally open, you
should see the meter reading drop to near zero when the links are closed.
If the reading doesn't change, then obviously the link isn't shunting
current away from the meter. Some meter cases have 'finger blades' that you
pull to disconnect the meter and short leads at the same time. So when you
pull the 'blade', the meter goes to zero, even if the shorting fingers fail.
These types of cases have been around since Westinghouse, shorting-link
failures are very rare in this type of unit (after all, it isn't rocket
science, they designs are simple and robust).
Some CT's have a thin (mica?) member between the secondary terminals. If
inadvertantly open-circuited while energized, the voltage spike will
'puncture' the insulation member and allow an arc to jump across the
terminals right at the CT. Have to replace the CT to repair it, but the
high voltage won't be sent through metering lead damaging other components
(or people). Not *all* have this feature.
daestrom