| But it sounds like the 120v coil is used to detect mains failure, power
goes
| out, relay loses power, contacts open/close, triggering the alarm. The
relay
| can be left alone, you only have to mess with the low voltage signal it
| switches.
If he wants to use a cap to delay it the lower power the better. Even a reed
relay will work OK and keep the cap size down. That's the key - run from a
rectifier circuit.
N
It seems to me that the OP would prefer to use what hardware exists
now in order to minimise expense and the complexity involved in a
complete re-design of what he now has. The relay he is using now is a
3 pole changeover unit so depending upon what is currently connected
to the relay contacts will have some bearing on what he can do in the
easiest and most cost effective manner.
However, using a reed relay to detect the mains failure would involve
using an additional step-down transformer in order to supply the ac
sense input to the reed relay/rectifier/capacitor arrangement. While a
reasonable delay might be achieved it certainly would not be in the
order of more than a minute at most even if the reed relay coil was
10,000 ohms and a 10,000uF capacitor was used.
Assuming the OP did not want to alter the existing KUP relay or
wiring, the reed contact would be connected in series with the
existing 120Vac coil of the KUP relay so that the latter acted as a
slave off the reed relay. This would also mean that a separate
no-break 120Vac supply would have to be present to maintain the KUP
relay operated until after the reed relay contact had opened at the
end of the delay. Clearly, the need for a separate no-break 120Vac
supply was not on the OP's agenda, although a UPS could be used for
such a function.
Reed relay contacts are not intended to switch high voltages such as
120Vac and they don't like to switch ac current in inductive circuits.
The contacts quickly weld together or become pitted very quickly so a
reed relay contact would not be suitable to open the existing KUP coil
circuit. Even if the OP altered his existing KUP relay coil for a low
voltage dc unit capable of being switched by the reed contact, the dc
supply to hold the KUP relay operated AFTER the 120Vac mains had
failed would have to come from somewhere. Again, this would require a
separate no-break dc voltage source so this is even more complex than
using a UPS with the existing KUP relay. In this case a rechargeble
battery could be used but this would require that a battery charging
circuit would be required to maintain the battery in a fully charged
condition. All in all, it would be more expensive and there would be
no real advantage over sticking with the existing KUP relay and
providing a UPS.
If the OP really needs a delay exceeding 1 minute then the only way is
to incorporate a true delay-off relay as the ac sensing device and
slave the existing relay/s from this. He will still have to provide a
separate no-break 120Vac source (eg, UPS) to keep his existing KUP
relay operated though.
I would suggest the simplest method to achieve what the OP requires is
to first get a UPS of say 150 - 300VA rating and use this to supply
the existing KUP coils via the contact of a true delay-off relay such
as
http://www.artisancontrols.com/pdf/4390.pdf A 4390A-E would give
him an adjustable 30 - 300 seconds delay and the allow its input to
sense the 120Vac mains supply. Several KUP relays (assuming more than
one) could be handled by the delay-off contact since it has an 8A
rating.