We are using centre tapped transformer - 9V-0-9V /500mA for power supply. Circuit I made as below. For 200mA load , I am getting Vload is "4.5V" only. Let me know where is the issue , it has to work for load 9A/500mA right.

Or transformer is faulty, tried with two transformer , result is same.
upload_2018-6-26_9-25-2.png
 

(*steve*)

¡sǝpodᴉʇuɐ ǝɥʇ ɹɐǝɥd
Moderator
So therefore about 20V across the ends of the windings?

What does it measure with the load connected
 
The readings you give are consistent with a 4.5-0-4.5V (i.e 9V centre-tapped) transformer. This is NOT THE SAME as a 9-0-9V transformer.

Have you checked that the primary voltage is correct i.e. you're not running a 240V primary on a 120V supply?
 
Is the phasing of the transformer secondary's correct?
Using the notation: S = Start of winding and F = Finish of winding, the secondary must be connected in the order:
S, F, S, F. Otherwise the secondary's will effectively be in parallel which means that it is giving half wave rectification rather than full wave. If this is so, your output voltage will be 9V - forward drop of diodes, assumed to be 1V x 0.637 which calculates to 5.096V.
 
That transformer construction automatically has the wiring done by the manufacturer, so that its going to have proper series phasing relationships.
Any chance that you made a boo-boo on one diodes polarity of installation, or that you have one open diode ?
How much capacitance is the main filter and is your load resistor in the order of 20 Ω' s ?
 

(*steve*)

¡sǝpodᴉʇuɐ ǝɥʇ ɹɐǝɥd
Moderator
As best I can tell, he is posting from a place that has 220V (ish) mains.

Or more accurately "is no longer posting from..."
 
Top