Hi!
I need to power a led installation.
3298 leds * 60ma = 200A // 12v // 2400W
I have 4x 12V 60A power supplies for this. (see photo)
There are 13 different led strips lines, with different amount of led's per line. The idea is to connect them to each power supply so that the power requirement is distributed as even as possible.
Do you have some feedback on this?
Should I add a switch-on current limiter? in which case, how do I calculate which one to use?
thank in advance for the feedback!
I need to power a led installation.
3298 leds * 60ma = 200A // 12v // 2400W
I have 4x 12V 60A power supplies for this. (see photo)
There are 13 different led strips lines, with different amount of led's per line. The idea is to connect them to each power supply so that the power requirement is distributed as even as possible.
Do you have some feedback on this?
Should I add a switch-on current limiter? in which case, how do I calculate which one to use?
thank in advance for the feedback!