Phil Allison said:
"Bruce Varley"
** The general definition of Power Factor is the ratio of Watts to VA.
ie PF = Watts / VA
where V = rms voltage
and A = rms amps.
( Notice there is no mention of " cos phi" )
So, since the AC supply is a 240 volt rms sine wave
- VA is determined by the rms amps draw alone.
Consideration of phase angle or " cos phi" ONLY applies where the
current draw is also a sine wave.
See:
http://en.wikipedia.org/wiki/Power_factor
In a nutshell,
PF compares how hot cables get to watts consumed.
The ratio of 1 then equates to " good as possible ".
...... Phil
Thanks for the clear definition, Phil. I hope people will bear with me while
I take this a bit further.
I thought this formula would calculate a PF of 1.0 for a nonlinear load
typical of an SMR waveform, with sharp current spikes around the voltage
peaks, but fortunately decided to shut up and try a few simulations before
making any more comment. To my surprise, when I applied Phils formula to
such a current waveform, I came up with a 'result' (whether it's 'power
factor' or not is a very moot point) that is well under 1.0.
Why is this so? The reason a PF in the sinusoidal (linear, reactive load)
situation is low is that the voltage and current are out of phase, so that
there are portions of the cycle where the voltage and current are opposite,
and the reactive load behaves like a generator, returning energy back to the
source. So on average, the energy dissipated in the load is less than the
total volts * amps. But with the SMR waveform, the voltage and current are
always of the same sign at any one instant, so there is no time when energy
is being passed back from the load ot the source. Shouldn't the PF be 1.0?
I can't come up with a clear explanation for the result yet, it might be
just a mathematical artefact, with no clear physical significance.
Is this important? IMO, yes. Because we're talking of two completely
different loss mechanisms, that may require quite different approaches for
mitigation. In the case of true, low PF, the losses are due to that excess
current, that heats the transmission system up but doesn't show on your
meter and doesn't do anything useful (ignoring reactive power system
stability issues). In the case of the nonlinear load, the problem is the
nonlinear effects, of which 'harmonics' might be only part of it (because
superposition doesn't apply, if you want the technical reason for that).
Conventional PF correction is unlikely to help here, in fact providing nice
big fat caps to help the high frequencies to circulate could well make
things worse. I don't know what you do for a power network driving millions
of switchmode devices, all the way from tiny phone chargers up to big VVVF
drives.
All this might be related to whether it's smart policy to chuck out trannies
and light bulbs too...