Warren, are you sure that it doesn't say Kw and not Kv? It makes a
major difference in the interpretation.
If it is Kw, a 6.4 Kw load operating at 240 volts resistive load will
draw 26.66 amps as you correctly deduce.
While you could operate it from a 30 amp breaker, you may run into
intermittent trip problems with the breaker when the oven is running
at full capacity for an extended period of time. I'd personaly go for
the next higher capacity breaker, be it 40 or 50 amps, but be sure to
size the wire guage accordingly.
For 50 amps, I'd run #8 wire, although #10 may marginally satisfy NEC
requirements (I don't have a copy of the NEC handy here at home).
Another factor is the distance between your distribution box and the
oven, but I'm assuming that it is less than a 50-ft wire run. Realize
that the cost of the wire is likely the least expensive thing in the
project, because that wire will likely be there to provide service for
many years.
Licensed Electricians, please correct me if I'm wrong here, because I
don't want to steer the guy in the wrong direction and most of my
practical experience here is with 3,000 MCM or larger traction power
cables on subways and #24/26 signal and communicatons wiring. I also
generally assume that #14 is used for 15 amps, #12 for 20, and #10 for
30 amps, so I'm not entirely sure that #8 is adequate for a 50 amps
(but didn't want to suggest #6 which many homeowners have problems
working with).
My personal preferance here would be for a 40 amp breaker feeding #8
wire, however I'm not sure if 40 amp breakers are readily availble for
domestic distribution panels, but I know that 50 amp breakers are.
Then too, I'm a control system guy, so what do I know!
Harry C.