Measurement wire is used only for a few cm where the heat gradient is the
highest. Its alloy is accurately controlled to produce the exact seebeck
coefficient. Extension wire can be of much poorer quality, since there is
very little voltage produced across it.
Not just "quality", it's actually a totally different alloy in the
case of precious-metal T/C's. But note that there can be 50 or 100°C
difference between the "head" temperature and the isothermal block
temperature at the instrument, and the compensating leadwire must not
cause undue inaccuracy in the temperature reading due to that
temperature delta. Obviously if you eliminate the T/C itself and short
at the head terminal block the extension wire will not add any
additional error (i.e. will read the head temperature with the same
accuracy).