The "salesman" told me that because the pure sine wave inverter had a larger
tranformer it would be better able to handle thesurge. It definitely was
much heavier than my modified sinewave inverter.
Did he also tell you Saddam had WMDs? Same reasoning is being used
by the salesman.
Let's first look at numbers. For example, this modified sine wave
output is two 200 volt square waves with a spike of up to 270 volts
between those square waves. This is perfectly fine for computers
because computers are so robust. But this may also damage some small
electric motors due to what is in those output waves - ie harmonics.
There is no pure sine wave inverter. There are just 'cleaner'
outputs. Increased harmonics means hot spots inside a motor. That is
completely irrelevant to your problem - starting that fridge. It may
be 70 watts. But it also has a massive 'power on' surge. Electric
motors (unlike electronics) don't like low voltage during power up - a
slow response to a load change. Can your inverter supply new current
demands quickly?
Meanwhile, other problems include what controls that motor. Are its
electronics made upset by electricity provided with multiple
frequencies (60 Hz, 180 Hz, 300 Hz - all provided simultaneously)?
Long before anyone can answer, first the problem must be
identified. It does not start? If symptoms don't come with 'whys',
then every action will only be speculation. Is this fridge nothing
more than a motor and a mechanical thermostat? Or does it contain
other components? What do specs say for that fridge? Unfortunately,
most numeric specs for refriges are poor. Still, required are those
numbers and facts.
There is no bigger transformer. If the unit is outputing 200 watts,
then it has a 200 watt transformer in both modified or pure sine
wave. Inverter must supply not just 70 watts but also the massively
higher power required, fast on demand, during startup. The pure sine
wave inverter is only three times more? Then what is it missing, or
is that modified inverter better than most? We don't know since even
numbers such as THD for both units were not provided. Start with
manufacture specs for everything. What kind of load is this refrig?