On 1/2/2013 8:48 PM, josephkk wrote:
On Sat, 29 Dec 2012 11:04:23 -0800, John Larkin
On Sat, 29 Dec 2012 12:20:01 -0600, John Fields
On Fri, 28 Dec 2012 16:05:49 -0800, John Larkin
Air compressor 1/2 hp motor rated 220v (2-wire, not 3-phase) @
15A. Distance
from load panel ~100 ft (as the conduit runs).
15A can be handled by 14 gauge, but I'd normally go with 12
gauge due to
start current.
With such a distance, is it recommend to up-scale the wire to 10
ga?
Thanks.
#12 is 1.6 mohms/foot. That's 0.32 ohms total. The short-circuit
current from 220 volts is almost 700 amps. A half horse is only
around
400 watts, about 2 amps. I'd use #14.
---
The short circuit current through the wire resistance is irrelevant.
It is not. If 700 amps is available, there's a huge margin for the
startup current for a dinky motor like this one. And plenty of current
to blow a breaker if needed.
No John Larkin, you are full of baloney on this one. I do the wire
gauge
for motor starts all the time. I(sc) is NOT used.
What matters is the stall current through the motor when it's
starting
up; no doubt the 15A the OP mentioned.
Exactly. It needs 15, we have 700. We don't need #10 wire.
Incorrect setup. What is of concern is the drop during motor
start. Not
motor run and not wiring fault conditions. The goal is to keep it
below
5% including all other losses to the service transformer. Generally
a 2%
to 3% drop during normal operation, and no more than 8% during motor
start, is allowed in the building, all the way to the main service
lugs.
I'm curious about this. Doesn't a motor draw about 6-10 times FLA during
start? If so, wouldn't that cause a 18-30% drop during start if you have
a 3% drop normally? Or, looking at it the other way, if you size for 8%
starting drop, your normal operating drop would be only 1.3%.
---
From the OP's example we have a 240VAC 1/2HP motor with a startup
current of 15A being fed through 200 feet of #14 AWG wire.
1HP is 746 watts, so if his motor delivers 1/2HP at the shaft and it's
80% efficient it'll be taking about 467 watts from the mains under
full load.
200 feet of #14 solid copper looks like about half an ohm, so we have,
for the startup case:
15A--->
240AC>---[0.25R]---+<------+
| |
[16R] 233V
| |
240AC>---[0.25R]---+<------+
Because of the wire resistance, instead of 15A in the circuit we'll
have 14.55A, and that will drop 233V across the motor.
233V is 97% of 240V, so there's only a 3% loss in the wire.
In the full load case we have this:
1.94A--->
240AC>---[0.25R]---+<------+
| |
[123R] 239V
| |
240AC>---[0.25R]---+<------+
so the loss is less than half a percent.