???? a 3000VA inverter is going to want 250A @12V input, assuming 100%
efficiency. There IS a reason why higher input voltages are used as the output
rating climbs. Even my 1000VA unit runs a 60V string of 5*12V.
I absolutely agree.
However, since the originator of this thread wanted something that was
easier to "fail-proof" I thought that less cells might be better (even
if larger amperage capacity).
My 350 watt UPS has a single 12v/6ah battery - which I guess means
that at full power it might draw 30 amps (not for long!). So maybe I
should have said about 50 ah for 3kw if scaled correctly.
But you are correct about input power. I suppose that most UPS's have
the "inverter" part running in sync with the grid power all the time,
and the battery only gets called on when the grid fails.
Perhaps a standard 48v inverter would be better, but then there is the
problem of "all those cells".
I guess in the end, as others have said, the best system is a regular
maintenance schedule of replacing batteries at a set time period.
If the regular batteries in the UPS were re-sited OUTSIDE the box, it
might be possible to a) prevent the heat from one battery affecting
the adjacent ones and b) monitor the individual battery voltages more
easily.