Tom Biasi said:
I didn't catch the original post but I thought that this may be a good time
to mention that lightning rods are/were not designed for direct hits. The
purpose is to keep the accumulated charge below a safe level.
Tom
---------------
Actually this is extremely questionable. Design that I know of is based on
the probability of the stroke striking the rod rather than the protected
area. Granted, in some situations, particularly with tall structures, such
draining does occur (possibly increasing the chance of side flashes-another
problem) but this is a bonus, not the basis for design.
I am aware of a purveyor of lightning protection that claimed that his
protection works on the basis of charge dissipation. I have seen no evidence
that it does. I have no idea if he is still is in business.
Generally the source of the charge is several miles overhead -the rod
doesn't get seen by it. When a leader gets near a rod then it may be a
preferred target for the next step and if it is, then the main stroke will
be to the rod-if not something else gets hit. Design is based on it being
such a target for higher current strokes (but not necessarily lower current
strokes). This is true for protective systems for transmission lines as
well as structures. Catch the damaging strokes know that some of the little
ones will get by.
References:
Moussa & Shrinivasta, "Shielding of Tall Structures Against Direct Lightning
Strokes" Canadian Conference on Electrical and Computer Engineering,
Vancouver, BC, 1988
Energy Systems Journal, Vol. 11, N0.1 1991
EPRI Transmission Reference Book, 345KV and Above.
I believe that IEEE changed its standards to reflect the concepts involved
in these references.
Sorry that I do not have more recent references but I have been retired for
some time.
I agree with Vermin on the lack of usefulness of the ball. There appears to
be no rational basis for its use. Note that its thermal mass is generally
pretty small and by the time it starts to dissipate heat, any damage is
done.