Lightning protection for outdoor ethernet Grounding rod questions etc..

  • Thread starter Michael Kennedy
  • Start date
M

Michael Kennedy

I have a ethernet cable that runs from my house to an out building at my
house. I live in Florida and we have a real problem with lightning around
here. I plan on using a a TII telephone lightning arrestor on each end.. I'm
talking about the kind that the telephone company puts on the side of your
houese with the gas arrestors inside.

I think this will work but I have one problem.. I don't know if a ground
rod at the out building will be enough to ground a lightning strike. The
building doesn't have a ground rod right now but I was planning on putting
one in for this..

How do you get a good ground with a ground rod. I have tried driving one
down but when I ohm it there is always a lot of resistance vs the power
company's neutral / ground. I was told that a good ground rod will have
about 15 ohms of resistance between the rod and the system ground.

I would just hook this arrestor up to the out building's ground wire, but
the ground and the neutral are tied togeather and I don't think there is a
very good ground out there because the ground on the CATV wire will shock
you if you touch it and a ground in the building out there. On the voltmeter
it reads about 3v between the catv wire ground and the bldg ground.. So I
think my ground is overloaded or has a bad connection at the breaker
pannel.. It has 2 legs of 120v and one neutral. There is no seperate ground
wire.

Thanks for any advice / help..

- Mike
 
S

Stan

}I have a ethernet cable that runs from my house to an out building at my
}house. I live in Florida and we have a real problem with lightning around
}here. I plan on using a a TII telephone lightning arrestor on each end.. I'm
}talking about the kind that the telephone company puts on the side of your
}houese with the gas arrestors inside.
}
}I think this will work but I have one problem.. I don't know if a ground
}rod at the out building will be enough to ground a lightning strike.

You are asking for trouble. A telco lightning arrestor might protect a phone,
while not protecting your PC.

Safest bet: go fiber optic outside...used fiber-optic-to-RJ45 adapters
aren't that much, and if you buy a piece of fiber with the ends already
on, you won't have to pay for attaching the fiber ends.

Stan.
 
L

Leonard Caillouet

If you drop a ground rod at the outbuilding it will need to be bonded to the
rod at the mains. Check the codes for the gauge of the wire needed.

Leonard
 
M

Mike Berger

It's not just lightning that will be a problem with this arrangement.
You'll get all kinds of induced pulses and currents in the wire.
If you have to use copper, use opto isolators. Better yet, use
fiber between buildings with a media converter if needed. Using
copper between buildings like that is asking for trouble.
 
J

jakdedert

Michael said:
I have a ethernet cable that runs from my house to an out building at my
house. I live in Florida and we have a real problem with lightning around
here. I plan on using a a TII telephone lightning arrestor on each end.. I'm
talking about the kind that the telephone company puts on the side of your
houese with the gas arrestors inside.

I think this will work but I have one problem.. I don't know if a ground
rod at the out building will be enough to ground a lightning strike. The
building doesn't have a ground rod right now but I was planning on putting
one in for this..

How do you get a good ground with a ground rod. I have tried driving one
down but when I ohm it there is always a lot of resistance vs the power
company's neutral / ground. I was told that a good ground rod will have
about 15 ohms of resistance between the rod and the system ground.

I would just hook this arrestor up to the out building's ground wire, but
the ground and the neutral are tied togeather and I don't think there is a
very good ground out there because the ground on the CATV wire will shock
you if you touch it and a ground in the building out there. On the voltmeter
it reads about 3v between the catv wire ground and the bldg ground.. So I
think my ground is overloaded or has a bad connection at the breaker
pannel.. It has 2 legs of 120v and one neutral. There is no seperate ground
wire.

Thanks for any advice / help..

- Mike
I would (did) go underground for this application. (Run a ground wire
along with the Cat5).

I had the same setup: outbuilding with house around 75' away. I buried
a 2" plastic conduit when I had my water line replaced; but one wouldn't
really need to bury it as deep as I did. A foot or so would be
sufficient for low voltage stuff...not so difficult in Florida's sandy
soil...a real BEAR in Tennessee clay. I ended up running two cat5's, a
12 gauge ground wire and RG59. I used on cat5 for networking, one for
three phone lines and the coax (of course) for cable. I actually had
originally run thinnet coax in there, but there was plenty of room for
everything. I had 360 degrees of bends in the system, so installed
access points where it came out of the ground.

I put in a nylon pull line when I installed the conduit, with plenty of
slack at both ends so I could pull either direction. Total cost for
plasitc conduit, connectors and glue was less than $100, IIRC. Alas, I
sold the property for development. I wonder if they dug up my conduit....?

I'd like to do the same at my home, but I'm looking at bedrock less than
three inches under the grass in places along the intended route.

jak
 
S

simon hanlon

Jak's got the right idea, definitely go underground with Cat5 and an earth
wire to get rid of the difference in earth potential. If there is no way
underground then go fibre. I can make you up a 2 core fibre cable with ST
style connectors any length you like. The only real cost is in the media
converters.
 
M

Michael Kennedy

Well the cat 5 has been ran for about 4 months now and has been working
without any problems. Would the ground be just for the difference in earth
or would it be to catch stray lightning also..

-Mike
 
S

simon hanlon

Just to keep the earth potentials the same, I installed a network point in a
building with a different earth potential than the one across the road on
the same network. Everytime you plugged the cable in you would get a small
spark and the network would crash.
 
W

w_tom

Overhead or underground makes little difference. Both suffer from
the same transient threats. You must do the same well proven,
reliable, and simple solution that the telephone company uses to
connect their building to every other building in town. Each structure
must have its own single point earth ground. Every wire entering /
leaving the structure must first make a connection to that earth
ground.

Locate the NID box (or equivalent) provided by telco. It also has a
'whole house' type protector. What is it earthed to. That (should be)
your building's earthing electrode. Telephone wire earthed for same
reasons that ethernet cable must be earthed.

For CAT 5, that connection cannot be hardwired to all eight wires.
Therefore we use a surge protector. Notice the only purpose of a shunt
mode protector - to make a connection to earth.

This industry professional demonstrates the concept with two
structures. Both structures have their own single point earthing.
Even the incoming underground phone wire is earthed where it enters the
building. And to make those structures even more robust, separate
earth grounds are interconnected:
http://www.erico.com/public/library/fep/technotes/tncr002.pdf

To earth the CAT5, one manufacturer provides an earthing protector:
http://www.tripplite.com/products/product.cfm?productID=151
Notice the essential green ground wire. That must make a typically
less than 10 foot connection to a single point earthing electrode - at
each end of the cable.

How frequent are such destructive transients? On average, maybe once
every eight years. In your locale, well, consider the number as more
frequent. A number that will vary significantly based upon conditions
such as geology.
 
D

default

How do you get a good ground with a ground rod. I have tried driving one
down but when I ohm it there is always a lot of resistance vs the power
company's neutral / ground. I was told that a good ground rod will have
about 15 ohms of resistance between the rod and the system ground.

Fifteen ohms isn't bad. I find that much in my dual ground telephone
wire.

With lightening the important thing is that you get into the ground in
a straight shot - no right angle bends - ideally the ground rod should
be directly below the lightning arrestor (and it doesn't hurt to put a
ferrite core on the wire into the house). Ground unused conductors in
the cable, at the point of use only.

Lightning is fast rise time pulses so you design in terms of good
practice for high frequency high power transmitters - large diameter
conductors and minimal inductance.

A great technique for an ultra low impedance ground is to take a 10
foot length of rigid copper water pipe and braze or solder a heavy
ground wire(s) to it (three inches from one end) and wash it into the
ground. Wash it below grade and just have the wire coming out of the
ground.

Adapt one of those plastic compression fittings used with "Quest"
brand tubing - it will mate with the rigid tube and a garden hose. Get
up on a ladder and turn on the water and the pipe will just sink into
the soil if there are no rocks. Can't find some plastic compression
fittings and you can use brass or just jury rig the hose to the pipe
with hose clamps.

It helps to cut the end of the pipe at an angle if you need to work it
around rocks. I have had no trouble sinking 20 foot copper pipe down
into the water table using that technique.

Some amateur radio operators pack the pipe with salt after it is in
the ground, then wash the salt down.
 
B

Bob

Why not just do wireless? A couple of the right Linksys or Buffalo, or
Belkin wireless routers run in WDS mode will get you encrypted ethernet
connectivity with no Ground Potential Rise issues.
 
B

Bob

Jeff said:
or bury the cable

Actually, burying the cable will do little to prevent damage. The problem is
due to a phenomenon known as Ground Potential Rise. Lightning striking
closer to one building than the other results in a voltage difference
between them with significant available current. The whole idea behind surge
suppression is to give this current a path to follow through something that
is not damaged by this current flow. This site http://www.gpr-expert.com/
explains the phenomenon. In my world, I have alot more to be concerned about
than lightning induced surges. Contrary to what some people say - "nothing
can be done about a direct lightning strike" - this is not true. Lightning
strikes occur routinely at my, and many other tower sites with no damage.
Lightning is a very short term event - microseconds. a #6 wire can carry the
full current of a lightning strike without burning open. That is not to say
the point of attachment - of the lightning itself - will not be damaged.

The simplest way to deal with the issue is isolation. This could be
wireless, or fiber as others have suggested. Effective surge suppression can
be complicated, and requires much more than "putting a surge suppressor
somewhere". The basics involve bringing power, and data into a building at
the same point. Applying surge suppression to all, and bonding all ground
paths to a single point. That is basically what's done on the side of your
house where the power, phone company, and cable TV tie their grounds
together. It sometimes isn't done well or at all.
 
B

Bob

Jeff said:
or bury the cable
Actually, burying the cable will do little to prevent damage. The problem is
due to a phenomenon known as Ground Potential Rise. Lightning striking
closer to one building than the other results in a voltage difference
between them with significant available current. The whole idea behind surge
suppression is to give this current a path to follow through something that
is not damaged by this current flow. This site http://www.gpr-expert.com/
explains the phenomenon. In my world, I have alot more to be concerned about
than lightning induced surges. Contrary to what some people say - "nothing
can be done about a direct lightning strike" - this is not true. Lightning
strikes occur routinely at my, and many other tower sites with no damage.
Lightning is a very short term event - microseconds. a #6 wire can carry the
full current of a lightning strike without burning open. That is not to say
the point of attachment - of the lightning itself - will not be damaged.

The simplest way to deal with the issue is isolation. This could be
wireless, or fiber as others have suggested. Effective surge suppression can
be complicated, and requires much more than "putting a surge suppressor
somewhere". The basics involve bringing power, and data into a building at
the same point. Applying surge suppression to all, and bonding all ground
paths to a single point. That is basically what's done on the side of your
house where the power, phone company, and cable TV tie their grounds
together. It sometimes isn't done well or at all.
 