Insufficient data received error in modbus

Hi,

I have a monitor which is programmed as modbus slave (RTU).

When I am connecting single device and checking the RS485 communication using Modbus poll and RS232 to RS 485 converter, it works fine. But when I connect another similar device in loop at that time it gives insufficient data byte error and CRC error.

For single device there is no problem but it gives error when I add another device. Please find attached text file.

Please advice what could be the problem.

Thanks,
Paddy
 

Attachments

  • commdata.txt
    3.5 KB · Views: 220
Last edited:
Hi,
The problem was occurring because of improper voltage (reverse voltage i.e. VCC is connected to GND and vice versa) to bias resistors.

Regards,
Paddy
 

KrisBlueNZ

Sadly passed away in 2015
Thanks for following up here.

So that error meant that when a device stopped driving the RS-485 bus, it would be pulled into a break state? And that causes the Master to report "insufficient data" and a CRC error?
 