| Unfortunately, the lightning arresters consist of three 20 kV units per
| phase, stacked in series. When this station had been used with a 12 kV
| input, the bottom two sections of each phase were jumpered to ground.
| Nobody noticed this (there's a whole story behind the problems at this
| utility that lead up to this f*k-up worthy of another post.
Technically, configured wrong. That and inadequate checklist/testing.
I'll look forward to the "another post" some day.
| It was quite an event. I was standing about 100 feet away. After the
| initial fault, the system breaker (about 20 miles away) de-energized the
| entire line. We stood there for a few seconds and, just as a few people
| were thinking about walking up to it, someone shouted, "Wait for the
| reclose!" Sure enough, the system operators had neglected to disable the
| reclose operation. About 15 seconds later, another fireball.
How long did it take to make the repairs and reschedule the substation
maintenance?