We have a requirement to use GFCI's on xmas lights where I work. Can't
keep many from tripping.Anyone have any experience with this? Do we
need GFCI? How can we keep the lights on?
Are they tripping due to actual earth leakage in wet surroundings?
If they are actually doing their intended job then there's not much you
can do other than segregate the circuits into smaller protected zones to
minimise the amount of lights that go out in affected areas. It might
also be a good idea to assess how your lights are constructed to see if
there is an intrinsic problem in the design.
As mentioned earlier, I do the lights in Glasgow's George Square, and
many of the lighting effects are over 10 years old and very problematic.
The whole square is permanently protected by a primary earth leakage
circuit breaker that has a high 1A setting and a short time delay to let
sub-protection attempt to clear the fault. In many cases where a fault
goes to earth, the local over-current protection kills the circuit
before the earth leakage protection is required. However most of the
faults are Live to Neutral (waterlogged festoon lampholders), so in
those instances the earth leakage isn't affected anyway.
The lower effects that are in reach of drunks and wilful members of the
public who climb over fences to reach them, are protected by secondary
earth leakage protection at normal levels for the UK (30mA instant).
Is this any help? Or could your problem be associated with using the
protection on the flashing side of circuits where the power is
continually cycling on and off. This could cause nuisance tripping of
ordinary RCD's or GFCI's.
Can you describe your situation in a bit more detail?