Hi everyone.
I've done some more research into the generator / UPS compatability
issue and can now say that I was totally on the wrong in my original
approach.
It took quite a bit of experimentation (and some serendipity) to
discover that the UPS isn't particularly concerned about the harmonic
content of the incoming supply voltage waveform.
The main parameters of concern to a UPS are the frequency (the
requirement being quite a loose tolerance of +/- 5% on either a 50 or
60Hz supply) and the voltage remaining within predefined set limits.
In my case, although the generator was running just beyond the upper
frequency limit as initially set up, this was quite easily adjusted, and
the real problem I was having turned out to a consequent of capacitive
loading on the generator's output.
Now, despite the fact that the generator design involved a conventional
2 pole rotating field energised via sliprings from an AVR module, it is
still susceptable to the self excitation effect derived from the leading
current due to the capacitor loading presented in the form of a pair of
4.7uF capacitors in the UPS's mains input circuit.
Effectively, this capacitive self excitation was hijacking the AVR
control by sending the output voltage right up to 280v, some 50 volts
above the AVR mediated setting.
What was happening was that the UPS would see the reappearance of the
genset supplied mains voltage at acceptable voltage and frequency and
attempt to switch from battery power back to mains, whereupon the
9.4uF's worth of capacitive loading would appear across the supply
causing the voltage to jump from its nice steady 230v to somewhere in
the region of 270 to 280v, way beyond the buck boost regulation range of
the UPS, forcing an immediate return to battery power allowing the
generator to once more stabilise at its AVR mediated 230 volt level
which then initiated another attempt by the UPS to switch back to mains
power and a repeat performance.
Now one way to mitigate this effect is to preload the generator output
with a suitably inductive load (an inductor wired across the output).
This will work but a 230v 50Hz rated 500mH (or lower) inductor is a far
from standard item. The best I could do was to parallel a bunch of 4H
transformer primaries (some 8 400VA transformers in all). This allowed
the unloaded UPS to switch back to generator power and remain in that
state but the loaded state would cause it to cycle between battery and
mains as before.
In this case, the problem is almost certainly due to the fact the load
actually consists of yet another UPS providing a second level of
protection to my computers and I suspect that this UPS, an Upsonic
UPS600, also has its own bunch of mains input capactors to further
agravate the capacitive loading problem. Unfortunately, I don't have the
circuit diagram for this model so can only surmise at the existance of
the extra capacitance.
I haven't, as yet, removed the redundent Upsonic UPS600 from the power
supply chain to test this theory but, when I do, I'm going to fit an
autotransformer in its place to reduce the voltage from a nominal 230
down to around the 190 to 200v mark to minimise damage to the VDR spike
protection components in the PC's PSUs.
Whilst this might provide a solution, I think the real culprits behind
this universally experienced UPS compatabilty issue are the cheapjack
penny pinching genset manufacturers who seem to have elected to use an
AVR circuit derived from automotive alternator design practice.
The automotive alternator doesn't have to contend with the possibility
of self excitation effect from capacitive loading due to the 3 phase
stator windings being directly connected to a 3 phase bridge rectifier
pack, thus allowing an AVR module that only needs to control excitation
current via a single series pass power transistor (effectively, half an
output stage) in just one direction only.
When the AVR has to contend with capactively induced self excitation,
it seems to me that it needs to be able to counter this effect and this
requires that the AVR is able to drive excitation current in _both_
directions. This can only be achieved with an output that can both
source and sink current which requires a push/pull output stage of two
series control power transistors as per a single ended audio power amp.
A 'drop in' enhanced regulator module capable of using the exisitng
excitation supply voltage and field assembly would need to be a bridged
output design (i.e. four output transitors). Although it might be argued
that this raises complexity and costs, the additional cost becomes
rather swamped out by the costs of the gross parts of the genset itself.
The complexity issue is a non- issue once a new module design has been
committed to mass production anyway.
However, the idea of using such an 'improved' AVR module might have
some fundamental flaw which I've not been able to discern (but which an
experienced genset designer might be able to point out), so I'd be quite
happy to listen to anyone who can put me straight on this matter.
So, for anyone else, whose dream of providing extended UPS runtimes
courtesy of a cheap petrol genset, have been well and truly shattered by
the genset/UPS compatabilty issue, there are two options that can be
tried.
The first being the fitting of a suitable 250mH mains voltage rated
inductor (230v 2 to 4KVA case) across the genset's output (inductive
loading is not a voltage stability issue) or else, figure out a drop-in
AVR module design capable of bucking the self excitation effect from the
capacitive loading of the UPS(es). This last _might_ be a non-starter
but the first does definitely work.
I have considered yet another means of addressing the issue. Since the
waveshape of the supply isn't particularly critical, fitting clipping
diodes across the genset's output to clip at 350v peak for a 230v supply
(and 180v peak for a 115/120v suply) might prove effective.
In practice, a stepdown transformer to allow 'amplified zenner diodes'
operating at lower voltages/higher currents would be a more workable
solution. the transformer leakage inductance helping to take the sting
out of the current spikes in the clipping diodes as well as countering
the capacitive effect.
That's three possible workarounds. Of the three, unless I _have_ missed
a fundamental flaw, the improved AVR module is the most elegant
solution.
HTH & HAND
I've done some more research into the generator / UPS compatability
issue and can now say that I was totally on the wrong in my original
approach.
It took quite a bit of experimentation (and some serendipity) to
discover that the UPS isn't particularly concerned about the harmonic
content of the incoming supply voltage waveform.
The main parameters of concern to a UPS are the frequency (the
requirement being quite a loose tolerance of +/- 5% on either a 50 or
60Hz supply) and the voltage remaining within predefined set limits.
In my case, although the generator was running just beyond the upper
frequency limit as initially set up, this was quite easily adjusted, and
the real problem I was having turned out to a consequent of capacitive
loading on the generator's output.
Now, despite the fact that the generator design involved a conventional
2 pole rotating field energised via sliprings from an AVR module, it is
still susceptable to the self excitation effect derived from the leading
current due to the capacitor loading presented in the form of a pair of
4.7uF capacitors in the UPS's mains input circuit.
Effectively, this capacitive self excitation was hijacking the AVR
control by sending the output voltage right up to 280v, some 50 volts
above the AVR mediated setting.
What was happening was that the UPS would see the reappearance of the
genset supplied mains voltage at acceptable voltage and frequency and
attempt to switch from battery power back to mains, whereupon the
9.4uF's worth of capacitive loading would appear across the supply
causing the voltage to jump from its nice steady 230v to somewhere in
the region of 270 to 280v, way beyond the buck boost regulation range of
the UPS, forcing an immediate return to battery power allowing the
generator to once more stabilise at its AVR mediated 230 volt level
which then initiated another attempt by the UPS to switch back to mains
power and a repeat performance.
Now one way to mitigate this effect is to preload the generator output
with a suitably inductive load (an inductor wired across the output).
This will work but a 230v 50Hz rated 500mH (or lower) inductor is a far
from standard item. The best I could do was to parallel a bunch of 4H
transformer primaries (some 8 400VA transformers in all). This allowed
the unloaded UPS to switch back to generator power and remain in that
state but the loaded state would cause it to cycle between battery and
mains as before.
In this case, the problem is almost certainly due to the fact the load
actually consists of yet another UPS providing a second level of
protection to my computers and I suspect that this UPS, an Upsonic
UPS600, also has its own bunch of mains input capactors to further
agravate the capacitive loading problem. Unfortunately, I don't have the
circuit diagram for this model so can only surmise at the existance of
the extra capacitance.
I haven't, as yet, removed the redundent Upsonic UPS600 from the power
supply chain to test this theory but, when I do, I'm going to fit an
autotransformer in its place to reduce the voltage from a nominal 230
down to around the 190 to 200v mark to minimise damage to the VDR spike
protection components in the PC's PSUs.
Whilst this might provide a solution, I think the real culprits behind
this universally experienced UPS compatabilty issue are the cheapjack
penny pinching genset manufacturers who seem to have elected to use an
AVR circuit derived from automotive alternator design practice.
The automotive alternator doesn't have to contend with the possibility
of self excitation effect from capacitive loading due to the 3 phase
stator windings being directly connected to a 3 phase bridge rectifier
pack, thus allowing an AVR module that only needs to control excitation
current via a single series pass power transistor (effectively, half an
output stage) in just one direction only.
When the AVR has to contend with capactively induced self excitation,
it seems to me that it needs to be able to counter this effect and this
requires that the AVR is able to drive excitation current in _both_
directions. This can only be achieved with an output that can both
source and sink current which requires a push/pull output stage of two
series control power transistors as per a single ended audio power amp.
A 'drop in' enhanced regulator module capable of using the exisitng
excitation supply voltage and field assembly would need to be a bridged
output design (i.e. four output transitors). Although it might be argued
that this raises complexity and costs, the additional cost becomes
rather swamped out by the costs of the gross parts of the genset itself.
The complexity issue is a non- issue once a new module design has been
committed to mass production anyway.
However, the idea of using such an 'improved' AVR module might have
some fundamental flaw which I've not been able to discern (but which an
experienced genset designer might be able to point out), so I'd be quite
happy to listen to anyone who can put me straight on this matter.
So, for anyone else, whose dream of providing extended UPS runtimes
courtesy of a cheap petrol genset, have been well and truly shattered by
the genset/UPS compatabilty issue, there are two options that can be
tried.
The first being the fitting of a suitable 250mH mains voltage rated
inductor (230v 2 to 4KVA case) across the genset's output (inductive
loading is not a voltage stability issue) or else, figure out a drop-in
AVR module design capable of bucking the self excitation effect from the
capacitive loading of the UPS(es). This last _might_ be a non-starter
but the first does definitely work.
I have considered yet another means of addressing the issue. Since the
waveshape of the supply isn't particularly critical, fitting clipping
diodes across the genset's output to clip at 350v peak for a 230v supply
(and 180v peak for a 115/120v suply) might prove effective.
In practice, a stepdown transformer to allow 'amplified zenner diodes'
operating at lower voltages/higher currents would be a more workable
solution. the transformer leakage inductance helping to take the sting
out of the current spikes in the clipping diodes as well as countering
the capacitive effect.
That's three possible workarounds. Of the three, unless I _have_ missed
a fundamental flaw, the improved AVR module is the most elegant
solution.
HTH & HAND