| In article <
[email protected]>,
[email protected]
| says...
|> | In article <
[email protected]>,
[email protected] says...
|> |>
|> |> >> Currently, the area around Vancouver BC. Other residential areas with
|> |> >> single-phase service: near Waterloo, Toronto, and St. Catharines
|> |> >> Ontario, near Montreal Quebec.
|> |>
|> |> >> Where do you live that has full three-phase MV on top of every pole on
|> |> >> every street in a residential area? And three transformers on every
|> |> >> pole that has a transformer?
|> |>
|> |> >The transformers aren't on every pole (every third), but the wires
|> |> >are. I see it all over. All you have to do is look.
|> |>
|> |> I *have* looked where I live. I've told you what I see (a single MV
|> |> wire on the top of the vast majority of poles in residential areas).
|> |
|> | Afghanistan?
|>
|> If I ever get there, I'll tell you what I see, if I make it back. But
|> I have read some descriptions that would suggest something like 380Y/220
|> for three phase.
|>
|>
|> |> The next level up the distribution hierarchy is 3-phase, so 3-phase
|> |> lines do pass through residential areas, but only one phase is tapped
|> |> for the line of poles down each street or alley.
|> |>
|> |> Again, where do you see 3-phase on every pole?
|> |
|> | Illinois, New York, Vermont (haven't looked here in OH).
|>
|> Maybe you should. You'll find a LOT of 208Y/120, some 480Y/277 (larger
|> buildings), and maybe some leftover 240D/120, as well as single phase
|> service in 240/120. But do take your camera if you are convinced there
|> are some "6 star" services around.
|
| They surely wouldn't be called that because it's a stupid idea.
I don't know what they would call it if they provided it. That name is
one I made up just to have a way to refer to it until someone picks or
reveals a better or already used name. You're the one that says it is
already deployed; so you tell me what they call it in your area.
|> |> Tell us some places.
|> |> Even when there are 3 phases, do the transformers occur in groups of 3?
|> |
|> | Sure.
|>
|> And how many lugs on each are wired up? Does each transformer have the
|> same number of MV bushings (whether that be 1 each or 2 each)?
|
| Never climbed a pole, but all three phases are used for Edison 240V
| service. How may lugs is that?
That depends on the exact service. In the typical case there are three
transformers forming a closed delta. The primary transformer will have
3 lugs used. This transformer has a 120/240 volt secondary and provides
the source of 120 volts. The other 2 transformers are wired to other
phases on their primary, and have 2 lugs used at 240 volts. One is wired
between one end lug of the first transformer and the high leg. The other
is wired from the high leg to the other end lug of the first transformer
forming the delta loop. The 2nd 2 transformers are not grounded. They
may have (probably do have) an unused center tap lug. A total of 4 wires
come off this setup to the service drop in question. These are the three
phases plus the neutral from the center tap which is grounded.
Other cases might be 240 volt delta without any Edison, or an Edison
service that has no three phase at all.
|> |> Or do you mostly get one transformer per pole, tapping only one of the
|> |> 3-phase MV lines? (That's what I see when there does happen to be
|> |> 3-phase distribution).
|> |
|> | One pig per pole, three wires going between poles, under the MV
|> | lines.
|>
|> That's single phase 240/120 of the Edison split phase variety. No three
|> phase services there.
|
| Bullshit! The three wires were the three phases. You could see the
| connections on the pigs.
If the service is three phase, they put the three transformers on the SAME
pole.
Sure, you could form three phase service by splitting the transformers up
on different poles and interconnecting the secondaries between poles.
In the extreme case, the middle pole could be getting 120/240 from one
phase one an adjacent pole, and 120/240 from the other phase at the other
pole, and merge them to have the full "6 star" at the middle pole. But
is that actually wired that way for any service drop? The service drop
would have 7 (SEVEN) wires if so.
|> Look for cases of THREE transformers, each with the same number of MV
|> bushings (either all have 1 or all have 2 each), and at least 3 LV lugs
|> connected on all three. If only 2 lugs are connected on all three, then
|> you have a wye system, usually 208Y/120 but 480Y/277 is possible (600Y/347
|> is very rare except in Canada). If 2 lugs are connected on 2 transformers
|> and 3 lugs are connected on one transformer, it is probably 240D/120.
|
| Exactly!
But that's not "6 star" at all.
|> Other possibilities also exist. Be sure to get a number of photos at many
|> different angles to get an unambiguous view of exactly how all the wires
|> are connected. If you see one with 3 lugs connected on each of 3 separate
|> transformers, where the middle lugs of each are connected together, and
|> all the outer lugs, plus the joined middle lugs as one wire, supply 7 wires
|> into whatever building is served, then be sure to get a LOT of photos.
|
| I'm not in the business of supplying your curiosity.
No, you are in the business of not knowing the difference between differnt
kinds of three phase service configurations.