|>|> One option is to use a three phase transformer where all three
|>|> secondary windings are 240 volt center tapped to 120/240 volts. What
|>|> you get are SIX separate hot phase wires, and a neutral. I'll label
|>|> the phase wires going clockwise as A,B,C,D,E,F. You can have 2 three
|>|> phase systems from this, connecting to A,C,E or B,D,F. They would be
|>|> 208Y/120. And you can have 3 single phase systems from this,
|>|> connecting to A,D and B,E and C,F. Divide the tenants that get single
|>|> phase three equal ways and this way they get genuine 120/240. This
|>|> is actually a bit more complex than the common systems (for example
|>|> you would have 3 separate distributions for the single phase). You
|>|> probably can't meter the whole thing at once.
|>|> But I'd prefer such a system, myself.
|>|>
|>|
|>| I am obviously missing something. How do you connect the center taps
of
|>| three windings together, and then connect them in a wye, and not blow
up the
|>| transformer? And how do you get 240/120 & 208Y/120 from the same
windings?
|>
|>Maybe an ASCII art picture will help:
|>
|> B C
|> \ /
|> \ /
|>A----N----D
|> / \
|> / \
|> F E
|>
|>A-N and N-D are both wound on the first core. B-N and N-E are both
wound
|>on the second core. C-N and N-F are both wound on the third core. A
third
|>of the 120/240 loads would be served from A-N-D. A third of the 120/240
|>loads would be served from B-N-E. A third of the 120/240 loads would be
|>served from C-N-F. Half of the 208Y/120 loads would be served from
A,C,E
|>and N. Half of the 208Y/120 loads would be served from B,D,F and N.
|>
|>You could also get 120 volts from A-B or B-C or C-D or D-E or E-F or
F-A,
|>but you would not want to.
|>
|>You could also ignore the center tap and rewire it for 416Y/240.
|>
|>If the windings can be split and wired in parallel, you could rewire it
|>for 208Y/120 with double the amperage.
|>
|>A transformer with dual secondary 120 volt windings on each of the three
|>cores would be quite flexible, being able to be configured for any of
|>these three systems (but you would have 12 wires coming off the cores on
|>the secondary side).
|
| I agree with Mr Kelly
|
| They use delta vee to save money, why would they do this 6 pole thing?
To serve a lot of 120/240 volt single phase loads AND keep phases
balanced?
It might depend on how large a building is involved. Suppose it is a 10
floor building with 9 floors that have 12 residential apartments, each.
Would you in the role of a utility engineer be satisified running single
phase service into that building? I would think not. Then would delta
with only one side having all the 120/240 loads really be any better?
What I would ultimately propose for such a project would be to bring in
480Y/277 to the building, run that to the elevators, and put single
phase transformers on floors 3 (serving 2-4), 6 (serving 5-7) and 9
(serving 8-10), fed from diverse 480 volt connections (480 to 120/240
volt single phase dry transformers are pretty common). Various outside
HID lights could also be fed from the 277 volts.
The risk of mixing the wiring with 6 phases is probably realistic. But
isn't that what color marking of conductors is for? Besides, the only
places to get that mixed up is between a common single transformer and
the place where the phases split into 3 sets of single phase. If this
concept had been chosen a long time ago and been an accepted standard,
I'm sure we would have a color code standard, now, for each phase angle.
If anyone does make a three phase transformer that could be wired for
either 208Y/120 or 416Y/240, my bet is someone with the know-how could
wire it for the scheme I suggested (although it might not have enough
outgoing terminal lugs, or enough conduit space, to do it).