Sir Allen Wiggins . . . . .
A repair technician informed me that it is $ 650 to change out.
OH-MI-GAWD
That either is being a full blown " maternally copulating " rip off . . . . "artiste"
Or . . . . . he jist plane don't evin knoes durt.
First thing I would be doing would be to take TRUSTY DVM in hand and placing in AC mode and shutting the AC power breakers off that feed this unit.
Then test from that Jones barrier strip from COM 24VAC to the RED 24 VAC to confirm NO power.
Then transition the DVM to low OHMS mode and then short the two test leads together to watch the meter transition and just exactly how a short / direct connection reads on your units display.
Then you place one of those meter leads across the exposed portion of the problematic Y terminal and move immediately to the back to the vertical male spade connector that is sticking up . . . . . if that is reading as a direct connection you might be the
luckiest person ever.
Now move over to the R terminal to the right and see if possibly they might have given the same treatment to that vertical spade connector.
If finding connectivity between that
male spade terminal and the
Y connection, a good alternative repair now, is to take the GREEN wire and install a female spade connector on it and plug into the male connector just to the rear . . . . . that you just tested.
CREEDENCE . . . .
This circuitry uses 5 small gauge wires that carry 24VAC at a minimal current.
Normal wire color coding is:
COM 24 (WHITE) is to be the shared grounding of the 24VAC supply connections
R is the hot 24VAC
. . . . . . .then the powering of
Y . . . activates your HEATING function
W . . . activates your AIR CONDITIONING function
G . . . activates the FAN action
I can't see what some yoo-hoo was doing / has done with the HEW-MUNG-US (overkill) ORANGE wire nut.
The NORMAL YELLOW wire that goes to the Y terminal might have been too short and he extended it with the added GREEN wire length.
You might check that all out . . . . I hope he didn't connectively involve the passing RED wire viewed in that cluster.
Looking at that Y terminal of the Jones barrier strip, I am seeing the flat connecting plate that connects to a tab that extends a bit to the back and makes a sharp right angle bend to pass straight down and pass thru the circuit board to then solder connect to the copper foil pad associated with it.
I have marked / YELLOW squared . . . .an unobstructed view of the same tab to the left and I marked / YELLOWED in the mentioned tab on the Y connection.
Down within the tabs center there is being a shoulder nut that has been crimped into place . . . .it installs somewhat akin to a pop rivet, using a pneumatic press on a production line.
I am surprised that it held and did not ultimately spin, as it takes some rotational torque to pop the head off from an 8/32 plated brass machine screw.
Its somewhat akin to the unit below but probably only had 10 threads internally and at the top entry point of the nut there is a thin metal sleeve that gets crimped down and it then folds flat outwardly, as you can see in the picture.
This similar rivet shown below, depends upon peripheral outward tension on longitudinal splines to hold the rivet in place.
My my next alternatte procedure would be to see if my curved set of surgical hemostats, with ribbed ends would just reach under the bottom of the barrier strip at sub Y position to the bottom
of that screws threads and then try to CCW it out in multiple 22 degree grabs.
BOARD MARKUP . . . . . .
Thassssssit . . . . .
73's de Edd
.....