Jon said:
So is the mains really 240V CT and our 120V comes from one one of those or
is it different?
In the U.S., 240 VCT, with the center tap grounded is the
normal residential service.
i.e. does 240V come from the transformer outside the
residence and the then for 120V only one side being used and the neutro is
from the CT and is grounded somewhere while the ground on a receptacle is
grounded again but at a different point(so there could exist a potential
between ground and neutral?)?
The 240 volt center tapped is the secondary of the pole
transformer (or on or underground distribution transformer).
The center tap is usually (in my experience) grounded both
at the transformer, with the under the pole and overhead
ground line, and also at the fuse panel (down stream of the
meter) with a ground electrode.
That ground electrode is also connected to the safety ground
system in the building. The fuse or breaker panel is the
only place that the neutral point of the system (the center
tap) and the safety ground system are to be connected
directly together.
The only potential difference there should be between the
safety ground at the receptacle and the neutral at the
receptacle is the load caused voltage drop across the
neutral branch (from power panel to receptacle) conductor.
However, during a direct fault between hot and neutral
(until the over current protection opens the hot side) the
neutral conductor drop may approach half of the normal hot
voltage. I say, 'approach', because some of the total lone
voltage will be lost in the distribution transformer impedance.