I have 3 APC UPS's and 1 Emerson here in our place. If I remove the
batteries, or have them go dead, they will not start. Apparently when the
power is off, if the batteries are not working right, they will not start
up. I cannot remember, but this may be in the instructions. I am not sure.
The bottom line is, in most models of UPS's from what we found, if the
batteries are not working right, the UPS will not start. If you are trying
to service an APC unit yourself, take care that they will not sell the
service manuals, or parts to outside service people. Because of this, when
we get these in for service, we ship them back to the APC rep. Infact, we
found it comes out cheaper than if we were to have our own people fix it, or
even for me to do it myself!
--
Greetings,
Jerry Greenberg GLG Technologies GLG
=========================================
WebPage
http://www.zoom-one.com
Electronics
http://www.zoom-one.com/electron.htm
=========================================
I am troubleshooting a bad UPS and am not sure if it is supposed to turn
on without batteries installed. Refer to thread "APC SmartUPS smoked
with new batteries" for more information on this unit. As of now, there
are no batteries installed and unit emits a weak squeal from speaker
while power button is depressed. There is no click of relays.