Note gentle reader that as per usual w_tom cannot quote my message in its
entirety but snips and misquotes to make an erronous point.
First I can recycle all these points because w_tom has not really answered
them (please feel free to skip past this section if you have read all this
before):
w_tom claims that a MOV based surge arrestor can provide 100% effective
protection.
Unfortunately there is not a MOV manufactured that can safely handle 1% of a
typical Direct Lightning strike - w_tom avoids posting links to Data sheets
for MOVs because he knows that I could point out that any MOV he could find
would have difficulty handling a near strike let alone a Direct strike.
w_tom claims that it is all in the Earthing....
Ironically w_tom actually speaks some truth here but what he neglects to
mention is that a single Earth stake will suffer an EPR (Earth Potential
Rise - I believe that in the USA this is known as GPR) of in excess of
100,000 Volts in a direct strike.
w_tom does not even understand the basic physics involved for Earthing -
this is why he so frequently refers to the 'Art of Earthing' because for
w_tom Earthing is an art not a science.
An Earth required to even begin to effectively shunt a Lightning strike with
a minimum EPR requires multiple Earth stakes bonded together with low
impedance cable/bussbars covering 1/4 of an Acre or more - is this practical
or cost effective in a Domestic situation ? nope ! - yet w_tom still claims
100% effective 'whole house protection' for domestic premises is not only
possible but inexpensive.
w_tom claims that Lightning does not come in via Phone lines as all Phone
lines in North America are adequately protected - this is another of his
100% Bullshit claims he then tries to squirm out and blame the home owner
when presented with evidence that a high number of injuries and some deaths
occour each year in North America due to folk using Telephones during
Thunderstorms.
Further more w_tom claims that Telephone exchanges never ever suffer
lightning damage - this in direct contradiction of the experience of anyone
who works in the Telecommunications industry. w_tom ignores the example
provided as an inconvenient Fact.
Next w_tom claims that MOVs have been adequate protection for Telephone
exchanges since the 1960's - he neglects to mention that the Exchange
Technology in the 1960's was mainly Relay based switching with a lot of
Step-by-step (and Strowger) equipment still in use. whereas modern exchanges
are primarily digital Micro-processor based and these Micro-processors
running at up to 200Mhz routinely deal with Signals lasting just nano
seconds. The VLSI integrated circuits used in these Exchanges are
susceptible to static charges so small that a careless Tech who is not using
antistatic precautions when handling the Circuit boards in the exchange can
cause damage without even feeling or noticing the discharge.
w_tom from his standpoint of complete and utter ignorance then asks how
Spikes from Lightning lasting mere nano-seconds could not possibly cause
damage.
Further more modern exchange equipment does not depend on MOVs for
protection as while they may have been adequate to protect Strowger switches
they are neither up to the task nor reliable enough to provide protection
for modern exchange equipment so w_toms claim that lack of damage to
Telephones proves the effectiveness of MOV Lightning protection is also
proved False.
Modern Exchanges equipment typically uses an impedance of some sort in
series with the line to limit the current to managable levels then typically
a Transzorb or equivalent (Transzorb is a registered Trade name of Vishay
semiconductor however the term is often used to refer in a generic manner to
clamping diodes used for spike supression) to clamp the surge. This though
is not a techniique that can be readily adapted for use on low imedance
circuits like the AC power mains.
Next w_tom claims that a decently sized MOV does not suffer degredation -
again he provides no links to such a MOV's data sheet because all MOVs
suffer degredation when they suffer from surges - especially surges outside
the MOVs stated limits. But again w_tom knows that I can show that any MOV
that he posts a link to the data sheet for will suffer degredation and
possibly destruction in the event of a direct strike (and even in the event
of many near strikes) so he carefully avoids this inconvenient Fact *.
w_tom also claims that degredation of a MOV does not lead to it's clamp
voltage changing and the MOV becoming leaky - which leads to thermal runaway
in the MOV and ultimately its destruction - this in contrary to the IAEI
experiences and discussion paper on MOVs at
http://www.iaei.org/subscriber/magazine/04_b/04_b_brown.htm
But this is inconvenient data so w_tom just avoids it or misquotes it.
Finally w_tom claims that I think plug in Power protectors are effective -
This is just an insult and a Blatent lie on w_toms part
Next there are some questions regarding statements that w_tom has told in
the past that he has still not answered :
Tell me again tom what a Thermal Fuse is.
Tell me the fairy tale again about how Lightning is a 'Low energy event'
Identify the 'direct connection between AC mains and the Integrated circuits
in a modern modem' for me.
explain how 0.6mm diameter single strand copper wire has a lower impedance
than 2.5mm square multistrand copper wire and therefore provides a better
earth.
Tell me again how Telco gear and TV/Radio Transmitters never ever suffer
Lightning damage.
Tell me how long your 1KJ mov lasts in a Direct Lightning strike ?
how long does a surge last ? - what is the definition of a surge ?
Remind me again when the MOV was developed ? - I thought w_tom had finally
caught on to this one and I could leave it out but the latest posting
indicates otherwise
But then again I am probably assuming w_tom understands enough basic physics
to answer these questions.....
************************************************************
Now on with the rest of the show in which w_tom spins some more
misinformation -
Richard Freeman is so divorced from *why* as to even claim that call
centers use fiber optic cables. Yes? Call centers in the 1930s used
fiber optics? His diatribe is chock full of such spin.
w_tom is so stupid he quoted what I said directly - that MODERN Call centers
are fed by Fibre optic cable then he questions if call centers in the 1930's
used fibre optics?
- well I dont know about other folk but I hardly consider 1930's Technology
to be Modern. w_tom's Diatribe is chock full of such Lies and Misquotes that
you cannot really believe a word that he writes.
Even in the
1930s, earthing where phone lines entered the building meant operators
need not remove headsets during thunderstorms. Effective protection
was that well proven that long ago. Protection has always been defined
by earthing.
Ah just when I thought that w_tom had learnt when MOVs were invented he
regresses.
- As per usual w_tom misquotes and Lies in order to win points he so
desperately needs - a Clue here 'w' you are about 20 Years too early if you
are trying to use this to demonstrate how good MOVs are.
If you are trying to illustrate how important Earthing is well then again
you are trying to squirm in another direction - I have already pointed out
how important Earthing is that was never in dispute except in your mind.
What is in dispute is:
Your belief in the 100% effectiveness of MOVs for Lightning protection
Your belief that the lack of damage to Telephone exchanges proves that MOVs
are 100% effective (especially when Exchanges do not even typically use
MOVs).
Your assumption that an Earthing system adequate to to absorb a Single
Lightning strike without a signifcant EPR is not only feasible for the
average home owner but inexpensive.
Damage to telephone switching centers is so rare and so unacceptable
that damage is a major news story. Connected to overhead wires
everywhere in town, a switching station that suffers direct strikes
every year must never suffer damage. An informed technician would have
known this.
and Again w_tom shows that he knows nothing about Telecommunications and has
never worked in the Industry (or has he changed his tune slightly)
Lightning damage to Telephone exchanges does happen (Note I am not saying it
is common merely that it does happen) - despite the best Earthing and
Protection available In contradiction to w_toms continued and erroneous
claims of 100% effective protection.
Next w_tom assumes that this is big News- on the contrary it is so common
(Note that it is rare for a complete exchange Failure but individual Line
cards etc being damaged by Lightning is not an uncommon event following a
Thunderstorm) that equipment gets damaged in some way by Lightning that it
hardly rates a mention in the news and sparing for this is allowed for by
most sane Network engineers (Yes I do maintain a Stock of spares
specifically for Lightning damage for the ADSL Network I run - a clue to the
Aussies this network is currently about the third largest ADSL Network in
Australia).
Lightning damage is basically a calculated risk where you do all you can to
avoid it BUT it still happens from time to time as contrary to w_toms Lies
there is no 100% effective Lightning protection available and it is the cost
of doing business like all other failures in the Telco game (Back-hoe fade
etc ).
Numbers for direct strikes without damage were published
even in Oct 1960 by Bodel and Gresh in the Bell System Technical
Journal using data from New Jersey, Georgia, Maryland, and Michigan.
Must have been a damn thin issue of the Bell system Technical Journal In
October 1960!
Because we go from Volume 39 Issue 5 In September of 1960 which has the
contributer acknowledgements starting page 1379 to the Next article
("Signalling Systems for the control of Telephone switching") in Volume 39
Issue 6 starting page 1381 on November 1960.
It looks suspiciously like they did not publish a Bell System Technical
guide in October 1960!
Ooops have I just caught w_tom out in yet another lie ....
Effective and earthed protectors were standard that long everywhere.
Hundreds of surges were detected and measures - without damage to any
equipment. That is how standard protection - using earthing - has been
proven. This in direct contradiction to Richard's post - that provides
neither numbers nor citations.
Remind me again what Technology the Exchanges used in the 1960's ?
w_tom extraoplates that Because Strowger gear was less susceptible to Surges
and Lightning damage therefore modern computerised exchanges are also.
What does a telephone switching center do so that direct lightning
strikes every year do not cause damage? Every wire inside every cable
is earthed via 'whole house' type protectors located best up to 50
meters distant from the $multi-million computer. In 1960,
Hang on Computer based exchanges in 1960 ??? - there may have been one or
two but they were hardly common then.
that was the
MOV similar device that Richard says is too slow.
well actually w_tom is incorrect again. MOVs may have been used in the
1960's for Strowger exchanges but the Carbon block arrestor that he claims
in an earlier post was a MOV is actually a spark gap and this type of
arrestor also often included fuses or 'Heat coils'.
- once again because w_tom knows nothing about Telecommuncations he just
invented a few more facts to suit himself....
Gas discharge Tubes are generally used nowadays in Telephone exchanges
if/when surge supression is installed at the MDF (actually common in small
country exchanges) with semiconductor diodes (aka Transils, Transzorbs) used
on the Line cards themselves - Note Gas discharge tubes are unsuitable for
use on AC Mains which is why w_tom cannot rave on about them (just watch -
w_tom will devote the next post to why Gas discharge tubes are unsuitable
for Mains use and then pretend I said they were).
That up to 50 meter
separation increases protection.
He gets sooooo close and then misses the point entirely - geez if he had a
brain he would have worked it all out long ago. This is mainly due to the
way an Exchange is set up but effectively presents some Series impedance -
which was a point I raised.
Since earthing is so essential, then
every telephone company has long technical manuals on how earthing must
be installed, upgraded, and maintained. Earthing defines protection.
Well of course when w_tom says enough crap he has toget something right
eventually - Note though that he carefully avoids my statement that Earthing
was critical and where I pointed out that a Single Earth stake was woefully
inadequate to handle a lightning strike.
- but w_tom has been unable to answer any of the points I raised last post
so instead he makes up points he can answer
By this point, every lurker should know: no earth ground means no
effective protection. Richard Freeman is still posting four letter
insults
w_tom is is not a real name and is therefore an annonymous poster who goes
to great effort to hide who he is whereas I am a real person and use my real
name.
This is because at the end of the day w_tom is not prepared to stand behind
his advice.
so that you don't learn that fact and corresponding numbers.
Well w_tom does not quote facts, Numbers or even genuine articles as he
knows that they can all be shot down in flames So lets try a few of our own:
a Good ground resistance for a single earth stake is considered to be 5-10
Ohms
the current in a typical Lightning strike is 30,000 to over 200,000 Amps
Lets take the lowest Figures of 5 Ohms at 30,000 Amps
5*30,000 gives us an EPR of 150,000 Volts
what this means is that in the event of Lightning being shunted to the Earth
stake then the Earth stake will rise to 150,000 Volts above ground (at best!
at worst try about 2,000,000 Volts).
Of course w_tom will claim that Lightning is mysteriously different and does
not follow Ohms law but he will be as usual unable to explain why or prove
this.
No earth ground means no effective protection. Earthing - as
demonstrated by Ben Franklin even in 1752 - is the most essential
component of a surge protection system.
And as illustrated above single Earth stakes are inadequate (which is why
exchanges use multiple stakes) and multiple earth stake earthing systems are
not practical in most domestic situations so even if MOVs were 100%
failproof (they are not) you still would not be able to claim (as w_tom
does) that they offer 100% effective protection .......