There are some uses for having 2 separate circuits on a single receptacle
yoke. This is often done in kitchens to safely provide sufficient power
at one point when two appliances together would otherwise overload one
circuit. Many kitchen appliances can easily do that. Sometimes these
are wired as a shared neutral, either daisy-chained with other receptacles
or wired dedicated for maximum power availability. Or they can be wired
with separate neutrals. But in either case they must be switched off in
common at the breaker [210.7(B)]. With NEC 2008 now moving to near full
AFCI protection for dwellings [210.12(B)] there is a conflict. How do you
provide the required AFCI protection on a 2-pole (whether neutral is or is
not shared) 120 volt circuit? A 2-pole AFCI breaker would be required.
To date, only Cutler-Hammer makes these. Square-D does not, and in one
document, indicated they did not want to because that would encourage
shared neutral circuits (which are considered less safe). However, this
is still an impact even for circuits that don't involve a shared neutral.
How would _you_ wire a split-yoke dual-circuit 120 volt duplex receptacle
fed with dual-neutral wiring to the breaker originating the circuit under
NEC 2008 rules when the panel is a Square-D QO type?
yoke. This is often done in kitchens to safely provide sufficient power
at one point when two appliances together would otherwise overload one
circuit. Many kitchen appliances can easily do that. Sometimes these
are wired as a shared neutral, either daisy-chained with other receptacles
or wired dedicated for maximum power availability. Or they can be wired
with separate neutrals. But in either case they must be switched off in
common at the breaker [210.7(B)]. With NEC 2008 now moving to near full
AFCI protection for dwellings [210.12(B)] there is a conflict. How do you
provide the required AFCI protection on a 2-pole (whether neutral is or is
not shared) 120 volt circuit? A 2-pole AFCI breaker would be required.
To date, only Cutler-Hammer makes these. Square-D does not, and in one
document, indicated they did not want to because that would encourage
shared neutral circuits (which are considered less safe). However, this
is still an impact even for circuits that don't involve a shared neutral.
How would _you_ wire a split-yoke dual-circuit 120 volt duplex receptacle
fed with dual-neutral wiring to the breaker originating the circuit under
NEC 2008 rules when the panel is a Square-D QO type?