I have a 240 volt X 1000 watt device that runs from a 240 volt single phase power source. This device has 2 wires and the power source has L1, L2, & a ground (not neutral). The device is connected to the 2 hot wires. The device should pull 4.16 amps. When checking the amps with a clamp meter is the readout I’m seeing how many amps are going thru each wire or the entire circuit?
I want to put a fuse on this circuit but I don’t know if I should put a single 5 amp fuse on one leg to cover not going too far over the entire 4.16 amps or can I put a single 3 amp fuse on the leg to ensure not going too far over the 2.08 amps of that leg.
An understanding of this type of info would be great to know.
Thank you,