Confirm what?
We have calculated your total power availability and nothing you do in terms of rewiring in series or parallel connecting is going to increase the available power. It's 7920Whr. If you discharge the batteries in only 1/2 hour you can draw double (i.e. around 16,000W) or if you discharge it in ONE minute you can
THEORETICALLY achieve 475,200W. Won't be happening btw!
You need to consider what it is you want from the batteries. If it's a case of powering a home you need to know both the average consumption and peak consumption.
Most houses can run at a very low average level (say 1kW - lighting, fridges, hot water circulation, entertainment stuff etc permanently on - it can be more, it can be less - that's for you to figure out) but need a peak that can cope with hot water production (up to 3kW) cooking etc.
With an 8kW backup (like yours), if you can reduce the average level to (say) 500W you can run the house for 16 hours BUT every time you boil the kettle or cook you reduce that time a little.
So, what is your ultimate goal????