Phil Allison
** Hi all,
a repair job arrived last night accompanied a step-down tranny - the
repair is a US made amplifier that requires 120 volts AC at 60Hz - but
copes with 50 Hz all right.
The step-down tranny was supplied here in NSW by an eBay seller:
See: www.rhinotools.com.au
It is labelled as "2000W' and 240V to 110 V " plus the words "Korean
Technology".
The unit I have here is similar to ones on his eBay shop now, but not
identical.
Inside is a toroidal **autotransformer**.
Problems:
The unit cannot possibly deliver 2000 watts - the max continuous rating
should be no more than 500 watts. The resistance of the 240 volt winding is
5.6 ohms at room temp. Do the math.
The unit does not output 110 volts under load - tested with a 500 watt
resistive load, it outputs only 103 volts.
The only protection for the transformer is via a fuse holder on the back
fitted with a glass fuse rated at 10A - though the holder is not labelled
with any value.
Anyone smell smoke ??
..... Phil
a repair job arrived last night accompanied a step-down tranny - the
repair is a US made amplifier that requires 120 volts AC at 60Hz - but
copes with 50 Hz all right.
The step-down tranny was supplied here in NSW by an eBay seller:
See: www.rhinotools.com.au
It is labelled as "2000W' and 240V to 110 V " plus the words "Korean
Technology".
The unit I have here is similar to ones on his eBay shop now, but not
identical.
Inside is a toroidal **autotransformer**.
Problems:
The unit cannot possibly deliver 2000 watts - the max continuous rating
should be no more than 500 watts. The resistance of the 240 volt winding is
5.6 ohms at room temp. Do the math.
The unit does not output 110 volts under load - tested with a 500 watt
resistive load, it outputs only 103 volts.
The only protection for the transformer is via a fuse holder on the back
fitted with a glass fuse rated at 10A - though the holder is not labelled
with any value.
Anyone smell smoke ??
..... Phil