Determining if load is lagging or leading based on powers

Hello again guys, I have completed the question attached and also included the workings, but there are a couple of aspects to it that I just cant seem to understand, and was hoping you would be able to help me with.

The first part is in the first question, and it is how we are able to tell the Q1 is being absorbed and Q2 is being injected. Is this due to the fact the load 1 is lagging, so its reactive power must be being absorbed, and load 2 is leading so its reactive power is being injected?

For the second question, where has the equation for the apparent power come from? I understand the apparent power is equal to voltage multiplied by current, but why also multiplied by the square root of three? Is this due to the loads being Y-connected and making the equation for Vline be the voltage multiplied by the square root of three?

This pretty much sums it up, on a side note, I am having difficulty of understanding how the capacitor banks work so if somebody would be able to put some clarification down, I would be very grateful. As always, thanks for any help and if I missed anything out please let me know.
 

Attachments

  • Capture.PNG
    Capture.PNG
    81 KB · Views: 79
  • Capture1.PNG
    Capture1.PNG
    105.7 KB · Views: 117
  • Capture2.PNG
    Capture2.PNG
    95.1 KB · Views: 84
  • Capture3.PNG
    Capture3.PNG
    68.8 KB · Views: 83
The first part is in the first question, and it is how we are able to tell the Q1 is being absorbed and Q2 is being injected. Is this due to the fact the load 1 is lagging, so its reactive power must be being absorbed, and load 2 is leading so its reactive power is being injected?

Yes it is .
A lagging (inductive) load absorbs power.
A leading (capcitive) load injects power.
q.PNG



For the second question, where has the equation for the apparent power come from? I understand the apparent power is equal to voltage multiplied by current, but why also multiplied by the square root of three? Is this due to the loads being Y-connected and making the equation for Vline be the voltage multiplied by the square root of three?
Yes the square root of three ,
for Voltage in a 3 phase Y connection,when the voltage of the branch is needed.
note: the same applies to the Current in the DELTA case (par.e)

I am having difficulty of understanding how the capacitor banks work so if somebody would be able to put some clarification down, I would be very grateful. As always, thanks for any help and if I missed anything out please let me know.
Look at the "power triangles" above.
If QL=QC you are nulling the Q factor from the triangle,
and are left with only P(a pure resistive network) as the power company sees it.

What essentially happens is that the reactive power is "ping-ponged" between the inductors and capacitors in the exact amount for the power network not to notice their existence.
 
The first part is in the first question, and it is how we are able to tell the Q1 is being absorbed and Q2 is being injected. Is this due to the fact the load 1 is lagging, so its reactive power must be being absorbed, and load 2 is leading so its reactive power is being injected?
.

I don't understand the above statements. Reactive power, whether capacitive or inductive, both take return energy it from/to the circuit at twice the driving frequency. The net reactive energy difference is zero. I hope that is what you mean above.

Ratch
 