I have a 75KVA 600V delta to 120/208V wye dry type aluminum
transformer with a fairly high impedence rating of 7.5%.
There is a load of approx 90A across phase A and B and considerably
smaller loads on across BC and CA. The 90 amp load is one piece of
equipment.
I have 600V on H1 H2 H3 but only 200V across the AB phases.
The starpoint is firmly bonded to the ground, and all connections look
good.
Is there a tendency for imbalanced loads to further increase voltage
drop in transformers? I would suspect that I would have closer to 208V
on the secondary if the load was 90A on all three phases.
doug G
To send me e-mail remove the sevens
from my address.