After having several (like 4) thermostats fail in a 6-year period, it finally dawned on me to check the voltage from the transformer in the air handler and I found it to be a bit over 28 volts (when it should be 24V). My condo building has 208V service. The transformer in my air handler is a 208/240V one and was wired to the 208V terminal. I removed the wire from the 208V terminal and connected it to the 240V terminal and then found the voltage to be 24.2V. This makes sense when you do the math: 208/24 equals (approximately) 240/28. A transformer just reduces ("transforms") voltage based on a ratio, correct? And that ratio is determined by the windings in the primary and secondary, yes?
Strange that connecting 208V to the 240V terminal would produce the correct 24V, but it could just be something funky about the transformer. And BTW of the 61 units in the building, MOST have had at least one thermostat fail so there is a common thread.
Anyway, it appears I have possibly solved the problem of the thermostats failing but my question is, will this cause any damage to the primary (or secondary) of the transformer? Thanks in advance!
Strange that connecting 208V to the 240V terminal would produce the correct 24V, but it could just be something funky about the transformer. And BTW of the 61 units in the building, MOST have had at least one thermostat fail so there is a common thread.
Anyway, it appears I have possibly solved the problem of the thermostats failing but my question is, will this cause any damage to the primary (or secondary) of the transformer? Thanks in advance!