Robert11 said:
Hi,
Thanks for reply; appreciate it.
Funny, you think you understand something, and then when you think about it
a bit more, you realize you really don't.
I am still, a bit, confused over yyour explanation, even though it
is very clear. Please bear with me, as I'm a bit out of my field here:
The 120 V circuits are, of course, Phase A to neutral, and/or Phase B to
neutral.
The 220 is Phase A to Phase B.
Forgetting for a moment that the wires wouldn't take it, but as a
hypothetical only, suppose
you had 150 amps at 220 V between Phase A and Phase B.
Are you suggesting that you could "still" pull more off of either phase (to
neutral) although at 115 V ?
No, he's not.
Do you now how many amps of load you have between 'Phase A' and Neutral?
Call that X. Do you know how many amps of load you have between 'Phase B'
and Neutral? Call that Y. Do you know how many amps of load you have
between 'Phase A' and 'Phase B'? Call that Z. The amps you'll see on your
incoming 'Phase A' wire will be X+Z. Keep this less than 150A. Well, keep
it less than 120A, because of the 80% factor others have mentioned. In
fact, keep it well under 120A. The amps on your incoming 'Phase B" wire
will be Y+Z. Keep this under 150A (120A) as well.
If this doesn't seem to make sense, it may be because of ac electricity and
phase angles (+ and - signs in the case of a 120/240V system where the
phases are 180 degrees apart).
The above is simplified, but for typical residential loads, it should be
adequate in terms of the math. If you're actually going to make decisions
with safety and/or monetary impact, you will want to get more info. There
are probably Code rules for determining demand. One thing that has a huge
impact is diversity. Say you had 400A worth of equipment and receptacles
hooked up on 'Phase A' in your home, you might find that the most current
you ever draw for any sustained period (say, 15 minutes) is 80A, because not
everything is on full tilt all of the time.
Hope that helps, or at least, doesn't make it worse.
j